Discuss Add extra 13A sockets to Cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
There is a severe lack of sockets in our kitchen.

We have a cooker control switch with a single socket in it, but no cooker connected.
Would it be possible to run extra 13A sockets off the cooker control circuit?
If so, would this need to be done by an electrician to be complient with regs?

Thanks.
 
If the cooker circuit is already protected by an RCD then adding sockets to that is quite reasonable and well within the regs, even if not the way you would start doing it. Care is needed as cooker sockets are usually allowed a higher current than common socket wiring cable so either the over-current protection needs reduced to match, or chosen cable & socket arrangement designed to ensure that it is not possible to overload anything.

However, without RCD protection then it should not be added under the current regulations (though some years back that was common). If you can post a photo of your CU (consumer unit = fuse box) and any immediately adjacent electrical stuff then folks here can give you a good idea if it is or not. Please redact any obvious identification names or electric meter serial number/barcode.

You would be far safer to get an electrician in to do this as they should verify the supply has (working!) RCD protection and properly test it before issuing a minor works certificate covering that.
 

Reply to Add extra 13A sockets to Cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
755
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
633
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock