Discuss Adding a portable petrol backup generator to the main switch board. in the Australia area at ElectriciansForums.net

Reaction score
0
Hi,

I want to add a change over switch so that a portable backup petrol generator can be used when grid power goes down. As it has in Victoria. On referring to AS/NZS 3010:2017 to connect a portable generator. Figure 4.3 on page 57 shows a 1 pole Circuit Breaker in the active wire between the Change over switch and the 3 pin Appliance-inlet. With the neutral wire going from the change over switch direct to the 3 pin Appliance-inlet with no Circuit Breaker inserted in it. That is the Circuit Breaker is only in the active wire only and not in the neutral wire.

Yet section 4.3.2.3 Current limiting of incoming supply on page 53. Indicates:
Each incoming supply to the installation from the generator set shell be protected by a separate overcurrent protection device located within the electrical installation and, operating in all live (active and neutral) conductors. That is to use a 2 pole Circuit Breaker that is in both the active wire and neutral wire going to the 3 pin Appliance-inlet,

Which is correct. Is Figure 4.3 that shows a 1 pole Circuit Breaker in the active wire only. Or section 4.3.2.3 that indicates that a 2 pole Circuit Breaker in both the active wire and neutral wires that goes to the 3 pin Appliance inlet.

I think the correct answer is to use a 2 pole circuit breaker in the active and neutral going to the 3 pin Appliance-inlet. But am I correct?
 

Reply to Adding a portable petrol backup generator to the main switch board. in the Australia area at ElectriciansForums.net

Similar Threads

Just joined as DIY homeowner. I plan on buying a 10KW backup portable generator and using a transfer switch on the house in Riverside County. As...
Replies
2
Views
1K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
2
Views
91
I currently have a 100 amp sub panel for a 50 amp RV hookup (on a 60 amp breaker). This is about 100ft from the main with 2/4 wiring. Would a...
Replies
1
Views
919
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
I know it's not neat, but can I simply run a single extension cable from a small (3KVA) petrol, portable, inverter generator, positioned outside...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock