H

Helloworld1988

Looking for some assistance here as I have received different bids from different electricians. We live in Florida and have a Generator for emergency use, but have no way to power the house save for an extension cord currently. We are also remodeling our kitchen and are wanting to upgrade our main electrical panel (just adding more spaces as current panel (200 amp service) is full). I've decided that I want to do 2 (or 3 - depending on how you look at it) improvements that will satisfy these different objectives.

1) upgrading Meter panel to a Meter/Main Combo (200 Amp) located on side of house. This will be a GE tsmr820csflfmg with feed through lug
2) Include interlock kit on this New Main so as to facilitate Generator input (50 AMP). I will also be wiring up a plug in to feed the NEW Main.
3) Convert current Main Panel (200 Amp - 10 ft. away in garage) to sub panel.

I believe what needs to happen to convert the current main to a sub panel is that I need to separate the current ground and neutral on the old main, run a new ground wire off the NEW main panel to the Ground, making sure the neutrals and grounds are separated (neutrals must be isolated from the box) at the old panel.
The existing meter panel already has grounds. Would I need to replace these? Thinking not.

What am I missing?
 
Looking for some assistance here as I have received different bids from different electricians. We live in Florida and have a Generator for emergency use, but have no way to power the house save for an extension cord currently. We are also remodeling our kitchen and are wanting to upgrade our main electrical panel (just adding more spaces as current panel (200 amp service) is full). I've decided that I want to do 2 (or 3 - depending on how you look at it) improvements that will satisfy these different objectives.

1) upgrading Meter panel to a Meter/Main Combo (200 Amp) located on side of house. This will be a GE tsmr820csflfmg with feed through lug
2) Include interlock kit on this New Main so as to facilitate Generator input (50 AMP). I will also be wiring up a plug in to feed the NEW Main.
3) Convert current Main Panel (200 Amp - 10 ft. away in garage) to sub panel.

I believe what needs to happen to convert the current main to a sub panel is that I need to separate the current ground and neutral on the old main, run a new ground wire off the NEW main panel to the Ground, making sure the neutrals and grounds are separated (neutrals must be isolated from the box) at the old panel.
The existing meter panel already has grounds. Would I need to replace these? Thinking not.

What am I missing?
It sounds like you have it under control. Just remember that you are required to install an SPD On your main panel which stands for surge protection device and you will need 2 ground rods at least 6 feet apart
 

Reply to Adding New Meter/Main Combo in front of existing Main. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
387
Brian, DIY but 30-year commercial/industrial master HVAC tech. I have installed an emergency whole-house breaker switch next to my service...
Replies
1
Views
998
Good afternoon - we're considering adding an additional breaker to our "main service panel" which is where the meter is located. That panel has 6...
Replies
1
Views
663
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
724
Hi, I have a general question about main panel locations. The house is 120' long so I was contemplating running 2x 200amp panels located on the...
Replies
0
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock