Old Wylex rewireable cu, upfront RCD TT.
Client wants couple of extra sockets on kitchen circuit, running off extension reels at the moment.
if I put in extra sockets, do I need to bring cu upto regs as regards to division of circuits 314 etc. still not got me head round this bring circuits upto standard.
 
No you dont, just make sure your wiring and socket protective devices are upto current regs but do make a note on the certficate that whole installation is covered by single rcd.
 
You say up front RCD TT, if this is 100ma only then you will need 30ma for the ring main. In theory it may be best to change the consumer unit to a split board as I am assuming there is more than one ring circuit, this way you can put the ring circuits across seperate 30ma units,gives you some discrimination,
Cheers.
 
just carry on the ring from the other sockets you have in the kicthen and carry out a minor works cert for it, theres not alot to it really as you have the circuit protection covered with your RCD
 

Reply to Addition into kitchen circuit. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
I recently fixed a fault on a lighting circuit. The fault became apparent after some work I had carried out - I rewired part of the circuit for...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock