min size for bonding conductors on TNC-S is 10mm.
 
As Tel said by using the 115 value your not going wrong as your erring on the side of caution, all your going to do is get a higher CSA value which in anything under 16mm is not going to be that expensive. Once your starting to go over that and it's running 60-70 metres then it can become an expensive mistake

In your scenario I would not consider a single earth conductor taped to a single SWA as "bunched". if there were 6/7 SWA and 6/7 Earth conductors all taped together and run together, then to me that would be "bunched", and I would use start to use table 54.3 and the lower value for safety.

Ok. thanks, makes sense.
Actually I started all this to decide whether an installation I've looked at is ok. 10mm2 main earth and 4mm2 main bonding.
I think I can now safely say (pending a proper check of the Ze and fuse type) the 10mm2 main earth is fine but the main bonding could do with replacing, particularly as it magically turns from 4mm2 at the MET to 10mm2 at the water pipe! :-O

Thanks to all the other comments too, I am struggling to keep up with you all but I think it makes sense to me now.
 
TT can be as low as 2.5mm if protected. i need a holiday as well. was thinking of ireland this year, never been.
 
and see when you say a TT can be as low as 2.5mm (protected against mechanical damage)

is on the surface then going under the floorboards of a house covering mechanical damage in your mind..

the only tt instalation ive seen this is how it goes and i reckon is in 2.5mm
 
In a way, you do use the fuse trip current.
If you had a PEFC of 500A, with a BS1361 fuse, you would either have to use the values in the table (460A and 5s), or determine from the graph at what the actual disconnection time would be (about 1.5s).
Where people often go wrong, is they use the time value from the table, along with the measured value of PEFC. This results in a larger CSA than is necessary.

Spin - I was thinking about this myself but cannot find a graph in Appx 3 for a BS 1361 fuse. Am I going nuts?

For example, on my TNCS I have a Ze of 0.22 ohms. 230/0.22 = 1045 amps. Where am I checking my fault current against in the tables?

PP
 
Last edited by a moderator:

Reply to adiabatic on earth bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
709
Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock