Hi, I am looking for some advice.
I have been asked to quote for an installation where a generator will be used to supply occasional power to an installation that is not connected to the grid.
The IET says a floating earth generator needs to be modified to connect earth and neutral if more than one item of class 1 equipment may be connected. That is not practical as the installation will probably be in use long after the generator is changed, so the earth to neutral connection needs to happen in the installation to accommodate changing generators.
My current plan is to have a 16A CEEForm inlet to the fixed installation with the neutral earth link in the CEEform inlet, but there are two ways to provide the earth neutral link.
Option 2 will leave the earth between the generator and CEEform inlet as supplied by the generator, and the earth from the inlet onwards with earth connected to neutral.
There is also the option of leaving the connecting of earth and neutral until the small consumer unit, but I believe the sooner the better for this link. Am I correct?
Regards
I have been asked to quote for an installation where a generator will be used to supply occasional power to an installation that is not connected to the grid.
The IET says a floating earth generator needs to be modified to connect earth and neutral if more than one item of class 1 equipment may be connected. That is not practical as the installation will probably be in use long after the generator is changed, so the earth to neutral connection needs to happen in the installation to accommodate changing generators.
My current plan is to have a 16A CEEForm inlet to the fixed installation with the neutral earth link in the CEEform inlet, but there are two ways to provide the earth neutral link.
- Take the earth for the installation and connect it to the neutral and earth from the generator.
- Take the earth for the installation and connect it to the neutral from the generator only.
Option 2 will leave the earth between the generator and CEEform inlet as supplied by the generator, and the earth from the inlet onwards with earth connected to neutral.
There is also the option of leaving the connecting of earth and neutral until the small consumer unit, but I believe the sooner the better for this link. Am I correct?