Having been somehat involved in low-power off-grid and alternatives for 50 years, I think some people here are missing the point - although I absolutely agree that you do need to get this properly designed and the overall design formally approved before starting work or you may find the whole thing condemed when you try to get it connected. Two suitable cables in one suitable trench should be fine, but that is a trivial issue compared with what you are trying to do. I am not clear how you can "order 2 x 5kVA" supplies for use in dwellings. What you need, it seems to me, is effectively the equivalent of a private caravan site supply for 2 caravans from your main electricity supply. Those supplies can be privately metered and charged for by you and can be limited to 16 A or whatever - provided the right protection and voltage drop and required impedances are met. I would be surprised if they have been agreed to by the DNO (Scottish and Southern) as separate supplies for 'human dwellings'. Also, if people are to be living in them, they will also have to meet the Part P building regulations if the bungalow and the other house are to have internal 230 volt AC power supplied by these cables. I would suggest DC wired power only inside the two properties and the AC just to an external supplementary charger unit that only supplies DC to the buildings. It should be do-able, but in my opinion you need to get the whole scheme professionally designed and formally approved in detail before doing anything else!
p.s. the IET have a Code of Practice for LV and ELV Direct Current Power Distribution in Buildings, published in 2015, that you should probably read.
Hi, thanks for some constructive points, as you say some people are missing the point to the point of being offensive.
The two supplies were ordered as two new domestic supplies (the 5kva is what SSE have marked on the map) I know there is limited capacity locally on the network.
I have limited spare capacity on my own supply to cater for these two properties.
The cost of these new supplies is £400 each I then have the cabling costs. This compares with £40,000 to provide new supplies directly to the properties!
If I have a Tesla Powerwall (or equiv) and 5kw PV the internal AC supply would be supplied by this, the new supply would charge the Powerwall if there was insufficient from the PV, the new supply could also power MVHR , LPG boiler etc. The new house will be built to Passivhaus standards but not necessarily certified to that standard, but will be compliant with current building regulations.
I have some trenching information from SSE so I don't see any issues that I can't resolve trench wise. I am aware of voltage drop calculations etc but as I mentioned earlier the bungalow is currently on the end of a 350 metre 10mm SWA fused at 20A and has been for about 30 years!
Regards Jim
 
Look whatever you choose to do you still need an electrician on board at this early stage because you could do all of this yourself and find nobody will sign it off, some electricians can do third party certification, some can't, and some choose not too.
 
Look whatever you choose to do you still need an electrician on board at this early stage because you could do all of this yourself and find nobody will sign it off, some electricians can do third party certification, some can't, and some choose not too.
Hi, I do have a qualified electrician on board who has given me some guidance re trenching, is supplying the cable and will be terminating both ends.
Regards
Jim
 
Hi, I do have a qualified electrician on board who has given me some guidance re trenching, is supplying the cable and will be terminating both ends.
Regards
Jim
Good news - get them to do the design and you work under their supervision as an instructed person to install it. They will need to inspect at stages, then test, certify and obtain Building Approval.
 
Will there be any motors (of non trivial power output) supplied by this long run of cable? eg; vacuum cleaners, fridge/freezers...
 
Hi, thanks for some constructive points, as you say some people are missing the point to the point of being offensive.
The two supplies were ordered as two new domestic supplies (the 5kva is what SSE have marked on the map) I know there is limited capacity locally on the network.
I have limited spare capacity on my own supply to cater for these two properties.
The cost of these new supplies is £400 each I then have the cabling costs. This compares with £40,000 to provide new supplies directly to the properties!
If I have a Tesla Powerwall (or equiv) and 5kw PV the internal AC supply would be supplied by this, the new supply would charge the Powerwall if there was insufficient from the PV, the new supply could also power MVHR , LPG boiler etc. The new house will be built to Passivhaus standards but not necessarily certified to that standard, but will be compliant with current building regulations.
I have some trenching information from SSE so I don't see any issues that I can't resolve trench wise. I am aware of voltage drop calculations etc but as I mentioned earlier the bungalow is currently on the end of a 350 metre 10mm SWA fused at 20A and has been for about 30 years!
Regards Jim
The fact that cable has been there 30 years does not even mean you could replace it with like-for-like. Regulations have tightened a lot since then. Make sure that your electrician belongs to a Approved Scheme / Organisation that the local authority recognise as able to sign off new work. I am a professional electrical engineer with some 45 years practical experience, including supervising teams of electricians, but as I am not a practising member of an Approved Scheme I can't now sign off any domestic-related electrical work that needs local authority approval.
 
Hi, thanks for some constructive points, as you say some people are missing the point to the point of being offensive.
The two supplies were ordered as two new domestic supplies (the 5kva is what SSE have marked on the map) I know there is limited capacity locally on the network.
I have limited spare capacity on my own supply to cater for these two properties.
The cost of these new supplies is £400 each I then have the cabling costs. This compares with £40,000 to provide new supplies directly to the properties!
If I have a Tesla Powerwall (or equiv) and 5kw PV the internal AC supply would be supplied by this, the new supply would charge the Powerwall if there was insufficient from the PV, the new supply could also power MVHR , LPG boiler etc. The new house will be built to Passivhaus standards but not necessarily certified to that standard, but will be compliant with current building regulations.
I have some trenching information from SSE so I don't see any issues that I can't resolve trench wise. I am aware of voltage drop calculations etc but as I mentioned earlier the bungalow is currently on the end of a 350 metre 10mm SWA fused at 20A and has been for about 30 years!
Regards Jim
The fact that cable has been there 30 years does not even mean you could replace it with like-for-like. Regulations have tightened a lot since then. Make sure that your electrician belongs to a Approved Scheme / Organisation that the local authority recognise as able to sign off new work. I am a professional electrical engineer with some 45 years systems design, including maintenance, and loads of practical hands-on experience, including supervising teams of electricians, but as I am not a practising member of an Approved Scheme I can't now sign off any domestic-related electrical work that needs local authority approval.
 

Reply to Advice on long SWA cable run and new supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
894
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
776
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
785
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
739
Hi everyone, I intend to bury a 240 volt cable from my house to my barn about 7 metres as way. It will be buried under my tarmaced drive which I...
Replies
7
Views
340

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock