Discuss ADVICE ON TT OR TN-S FOR OUTSIDE SOLAR CABINET in the UK Electrical Forum area at ElectriciansForums.net

J L

-
Reaction score
2
Please see attached diagram, can someone advise on if this TT connection is correct for an outside solar metal enclosure as shown in the diagram? If not what are your recommendations on how you would do this please?
 

Attachments

  • SOLAR.PNG
    100.2 KB · Views: 21
As above - the armour needs connecting at least the supply end so ADS occurs if someone sticks a spade through it.

Are there any good reasons not to use the perfectly good TN-S earthing for the inverter?

If people are going to do tribal dances in the rain with bare feet while laying sacrifices on the cabinet you could add a local rod as an extra precaution.
 

Reply to ADVICE ON TT OR TN-S FOR OUTSIDE SOLAR CABINET in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
525
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock