Discuss Advice on what consumer unit to fit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hi ive been recently asked to wire a large property which has been specified to require 13 circuits
2 x 6amps
5 x 32amps
2 x 20amps
2 x 16amps
2 x 40 amps

Im just wanting some advice on consumer units, rcd and main fuse sizes

A 14 way consumer unit dual rcd would be ideal but im wondering how it works with rcd amperage, im aware each side of the board should be balanced out but should the amperage of each mcb total the amerage for the rcds?
 
look at the SBS CUs. aLL RCBO. no floppy links . RCBOs. loads of room to dress cables. a sparks dream machine.
1617915637509.png
 
Hi ive been recently asked to wire a large property which has been specified to require 13 circuits
2 x 6amps
5 x 32amps
2 x 20amps
2 x 16amps
2 x 40 amps

Im just wanting some advice on consumer units, rcd and main fuse sizes

A 14 way consumer unit dual rcd would be ideal but im wondering how it works with rcd amperage, im aware each side of the board should be balanced out but should the amperage of each mcb total the amerage for the rcds?
You might be better checking the loads, because even in a large property they could never use those loads on a standard 100A supply (nor would they ever get close to it I suspect). Are the 40As showers or hobs?

If there are lots of large loads, multiple showers etc that could be genuine regular loads then you may need to consider whether the main fuse is adequate.

RCBOs are probably better - if it's a large property then there should be something in the budget for a decent board that will last...

If they are really being tight, then maybe a Dual RCD Hi Integrity board, with RCBOs on some selected circuits...
 
look at the SBS CUs. aLL RCBO. no floppy links . RCBOs. loads of room to dress cables. a sparks dream machine.
View attachment 84374
what's between the busbars? just a bit of plastic? It would take me ages because I'd be having to constantly check I hadn't got one of the prongs the wrong side of the screw clamp.

Looks like it would be a dream to EICR though!
 
You might be better checking the loads, because even in a large property they could never use those loads on a standard 100A supply (nor would they ever get close to it I suspect). Are the 40As showers or hobs?

If there are lots of large loads, multiple showers etc that could be genuine regular loads then you may need to consider whether the main fuse is adequate.

RCBOs are probably better - if it's a large property then there should be something in the budget for a decent board that will last...

If they are really being tight, then maybe a Dual RCD Hi Integrity board, with RCBOs on some selected circuits...
Both 40amps are showers, do you think it would be better to get them to bite the bullet and go for a 14 way rcbo board?
 
what's between the busbars? just a bit of plastic? It would take me ages because I'd be having to constantly check I hadn't got one of the prongs the wrong side of the screw clamp.
These people are supposed to be specialist custom DB builders.

Surely they don't use 2 individual SP busbars for DP devices? It's not as if DP ones for single-module DP devices don't exist...
 
I'd personally say RCBOs are definitely the way to go - Fusebox are cheap enough to not get silly, and even the Hager ones aren't outrageous compared to what's being spent elsewhere I'm sure.

Type A RCBOs should mean it's not going to need any upgrading for a long while - until AFDDs are more widespread...

But that does sound a lot of load for a (I assume single phase ) fuse head, if those showers might both be used at once...

If there's ever likely to be additions (more than one EV for example), then might be worth investigating a Three Phase head.

You can get devices to mitigate overload with showers - where it won't let both draw 40A at once... David Savery has a video on it on youtube....
 

Reply to Advice on what consumer unit to fit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
I was just googling for skeleton boards after reading the last thread and various pictures of consumer units popped up, some wired terribly and...
Replies
6
Views
735
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock