You could use thermistor in-rush current limiters as I have done but you have to work out its required cold resistance and power rating and then faff about mounting it inside an enclosure which takes into account it gets hot.

You'd be better off using one of these ready made devices which can solve LED problems like yours:

ESB 101-23 - Peak current limiter, 23 A, 2000 µF - https://www.reichelt.com/gb/en/peak-current-limiter-23-a-2000-f-esb-101-23-p167632.html?CTYPE=0&MWSTFREE=0&PROVID=2788&wt_guka=54950995355_263550067601&PROVID=2788&gclid=EAIaIQobChMI9-a2i8za3QIVr7ftCh24QQA7EAQYBSABEgKcYvD_BwE&&r=1
 
Update!!

It was definitely in rush current!

I have not experienced it being a problem before as I only do domestic and Type C breakers are rarely needed.

I had taken in to account VD, worked out what the Zs was likely to be and used 6mm SWA for the approx 100m run.

My Zs is 1.45ohms.

I am picking up a Type C 6A and 10A tomorrow and will try those, however I did have a 16A Type B and this is working fine. The max Zs for 16A Type B is 2.2 ohms so I have been saved.

I can run another circuit for the next 5 x 200W lights or I might find that a 20A type B works for all 10 lights as long as the Zs < 1.75ohms.

I'm embarrassed that I didn't factor inrush current in to my design, it's not acceptable to be acting reactively like this to a problem that should never have arisen!

One last question..

What is the relationship between Type B and Type C MCB's with regards inrush current? What I mean is if for example a 6A Type B could take perhaps 100A for 0.2s without tripping what would the equivalent be for a 6A Type C be? Is there some data sheets on this or some interesting reading somewhere?

ps.. these are the lights http://www.belllighting.co.uk/fittings/SkylineProLEDFloodlightsWallpacks

Apparently the inrush current is approx 75A.
 
Update!!

It was definitely in rush current!

I have not experienced it being a problem before as I only do domestic and Type C breakers are rarely needed.

I had taken in to account VD, worked out what the Zs was likely to be and used 6mm SWA for the approx 100m run.

My Zs is 1.45ohms.

I am picking up a Type C 6A and 10A tomorrow and will try those, however I did have a 16A Type B and this is working fine. The max Zs for 16A Type B is 2.2 ohms so I have been saved.

I can run another circuit for the next 5 x 200W lights or I might find that a 20A type B works for all 10 lights as long as the Zs < 1.75ohms.

I'm embarrassed that I didn't factor inrush current in to my design, it's not acceptable to be acting reactively like this to a problem that should never have arisen!

One last question..

What is the relationship between Type B and Type C MCB's with regards inrush current? What I mean is if for example a 6A Type B could take perhaps 100A for 0.2s without tripping what would the equivalent be for a 6A Type C be? Is there some data sheets on this or some interesting reading somewhere?

ps.. these are the lights http://www.belllighting.co.uk/fittings/SkylineProLEDFloodlightsWallpacks

Apparently the inrush current is approx 75A.
I had that problem once, inrush, you mucky people, some will get the joke some wont, not going to explain.
 
Not a cheap solution but if you had sequenced switching so that only three lights came on at any one time, with a 0.5s delay or so between each bank this would alleviate the inrush current problem. You could fit delay on relays set to different times for each light or I believe you can buy specific staged switching systems.
The thermistors are a problem because of the heat and they ought to be switched out after start up which is more expense and messing about.

The current difference between B and C (and D) is not something I have seen data on but logic indicates that if on heavy overload an MCB trips in 10 ms, then any current over the trip rating but faster than 10 ms will not give it time to trip. Therefore you need to slightly average the current seen on start up so if an LED has 150A for 0.3ms if may seem to the MCB to be only 50A (or less) over 10ms, in this case a B type would trip, a C type may well trip and a D type would not trip.
 
Glad you got it sorted out. Inrush current for switch mode power supplies / LED drivers is something that's not easy to calculate accurately. If you have a borderline case, which it sounds like yours was, whether it trips can actually boil down to how near the zero point the supply waveform happens to be when the switch closes and whether the lights have been recently run or not.
 
Just as a footnote, if you're planning to add more lights onto the same supply I'd suggest supplying them via a separate switch or timer or PIR or whatever switching system they're on, even if it works out more costly. That way they won't all switch simultaneously which would add to the inrush current issue.
 
Just as a footnote, if you're planning to add more lights onto the same supply I'd suggest supplying them via a separate switch or timer or PIR or whatever switching system they're on, even if it works out more costly. That way they won't all switch simultaneously which would add to the inrush current issue.
Thanks Marvo.
The plan is to have the next 5 on a separate switch.
I appreciate the detailed and informative responses, thanks again.
 
Well the 5 lights work fine on either a 10A Type B or a 6A Type C, so I should be ok with all 10 on a 20A Type B or possible a 10A Type C. Also the next 5 will be switched separately so that will avoid the inrush current of all 10 at the same time. Happy :)
 
Well the 5 lights work fine on either a 10A Type B or a 6A Type C, so I should be ok with all 10 on a 20A Type B or possible a 10A Type C. Also the next 5 will be switched separately so that will avoid the inrush current of all 10 at the same time. Happy :)
Until some body switches, all of the lights on at once, you just know it's going to happen Murphy's Law dictates this.
 
You can find the time Vs current curves for type b,c,d MCB in the installation and test regulations.
Type B instantaneous trip is 3-5 times rating
Type C instantaneous trip is 5-10 times rating
Type D instantaneous trip is 10-20 times rating

This is the magnetic trip and applies to inrush current.

I should add that the current is RMS current, so averaged over 1 half cycle. So very high inrush currents lasting less than half a cycle might not trip the MCB if the average over that cycle is lower than the trip characteristics.
 

Reply to Advice regarding inrush current please? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
894
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs). 6A breaker in Garage consumer...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock