I have just fitted 5 x 200w LED floodlights on the same switch.
I fitted 3 yesterday all worked fine. However the owner said they tripped once after I had left, no further info as to if they tripped immediately or after a while.

I have just fitted the last 2, the MCB is tripping immediately when the lights are switched on.

It also trips immediately when only 4 lights are connected.

At present they are on a type B 6A MCB.

The RCD does not trip and there is no fault to earth.

I had zero time to investigate and am returning in the morning.

My thoughts are.

1. Short circuit L-N
2. In rush current.

I know LED's can have a high in rush current, but could 3x200W LED floods (power factor 0.9) cause the MCB to trip? Could 4 or 5 cause it to trip with regards in rush current?
 
It's most likely to be the inrush current for the drivers. Typically these are switch mode power supplies which have a fairly high inrush current due to the sizeable capacitors and inductors they contain.

Providing standard testing rules out things like shorts, IR faults etc. I would upgrade the MCB to a Type C.
 
what size cable have you used? you could probably fit a 10A type C.
 
I have just fitted 5 x 200w LED floodlights on the same switch.
I fitted 3 yesterday all worked fine. However the owner said they tripped once after I had left, no further info as to if they tripped immediately or after a while.

I have just fitted the last 2, the MCB is tripping immediately when the lights are switched on.

It also trips immediately when only 4 lights are connected.

At present they are on a type B 6A MCB.

The RCD does not trip and there is no fault to earth.

I had zero time to investigate and am returning in the morning.

My thoughts are.

1. Short circuit L-N
2. In rush current.

I know LED's can have a high in rush current, but could 3x200W LED floods (power factor 0.9) cause the MCB to trip? Could 4 or 5 cause it to trip with regards in rush current?
The Btype OCPD can't handle the current inrush, try a C type as SparkyChick and Tel have indicated posts 2 and 3
 
Best check the R1 + R2 and the Ze and then fit the "best" MCB you can .... Tel's suggestion of a 10A type C is probably the way to go.

Do the MI's say anything about the limit on a circuit?

Is this the site where the client wants another 5 fitted?
 
As above, refer to the manufacturer re expected inrush current.

I'm yet to experience this phenomenon myself to be honest. Most led I have connected to one switchway was 6 x 200W hi-bays and a B6 didn't bat an eyelid.

Hence I have never used an inrush current limiting device, but I do know they exist if you are still experiencing problems after trying a C curve device.
 
what size cable have you used? you could probably fit a 10A type C.

I've used 6mm SWA due to the VD.

Best check the R1 + R2 and the Ze and then fit the "best" MCB you can .... Tel's suggestion of a 10A type C is probably the way to go.

Do the MI's say anything about the limit on a circuit?

Is this the site where the client wants another 5 fitted?

Nothing on the MI's about the limit on the circuit Murdoch.
Yes, there will be another 5 lights next year!

As above, refer to the manufacturer re expected inrush current.

I'm yet to experience this phenomenon myself to be honest. Most led I have connected to one switchway was 6 x 200W hi-bays and a B6 didn't bat an eyelid.

Hence I have never used an inrush current limiting device, but I do know they exist if you are still experiencing problems after trying a C curve device.

How does an inrush current limiting device work and how is it fitted Andy? Just incase I still have trouble with a 10A type C when the next 5 lights are fitted?
 
Nothing on the MI's about the limit on the circuit Murdoch.

Yes, there will be another 5 lights next year!

I would be researching the MI's for guidance - and if nothing is forthcoming you need to "prepare" your client for a higher bill as you will need to use a separate circuit for the next 5 lights
 
I have just fitted 5 x 200w LED floodlights on the same switch.
I fitted 3 yesterday all worked fine. However the owner said they tripped once after I had left, no further info as to if they tripped immediately or after a while.

I have just fitted the last 2, the MCB is tripping immediately when the lights are switched on.

It also trips immediately when only 4 lights are connected.

At present they are on a type B 6A MCB.

The RCD does not trip and there is no fault to earth.

I had zero time to investigate and am returning in the morning.

My thoughts are.

1. Short circuit L-N
2. In rush current.

I know LED's can have a high in rush current, but could 3x200W LED floods (power factor 0.9) cause the MCB to trip? Could 4 or 5 cause it to trip with regards in rush current?
https://www.mouser.co.uk/new/amphen...MI3_WfkqfZ3QIVg73tCh3DTgoREAAYASAAEgKcovD_BwE
 
Its very difficult even if you have the data, i have MIs quoting very very high inrush but for a very small time like 2mS etc but the current can be 60A for a small led light. Trying to work out the profile is too hard as you dont have the decay rate, just a peak which is often massive. I find trial and error works best, for MCBs go high and sluggish, like Cs and Ds. For relays or any switching device, use industrial strength relays or contactors. This is after a few years going back replacing presence detectors, dusk til dawn sensors and lightwave RF relay boxes.
 
How does an inrush current limiting device work and how is it fitted Andy? Just incase I still have trouble with a 10A type C when the next 5 lights are fitted?

I don't know for sure as I've never used one or researched one, but I suspect it's akin to a dimmer that gradually ramps up the voltage when first powered on (like the vPro dimmer modules).

By doing this, the capacitors and inductors on the input stages of the drivers have a chance to charge up to supply voltage slow and steady rather than the huge wallop you get from charging them up from nothing to 240v in an instant.

This is one of the benefits of switch mode drivers as typically many of them are capable of delivering full output load at a very wide range of input voltages.
 
Could have sworn I replied to this thread the other day....gawd knows where my post went.

This is a data sheet for a Meanwell 200w LED driver which is a popular unit used by quite a number of manufacturers.
I would imagine characteristics are similar for other brands.
They suggest 4 units on a 6A type B or 6 units on a 6A type C

ELG-200-MEAN WELL Switching Power Supply Manufacturer - https://www.meanwell.com/webapp/product/search.aspx?prod=ELG-200
Meanwell are one of the best brands of LED drivers available. I've used a wide range of their product line over the years and never been disappointed. It would be dangerous to assume that you could get insight into the performance or specs of another brand by referring to the datasheet of the Meanwell equivalent, I can almost guarantee the other brand will fall short and often by a large distance.
 
I've fitted eleven x 28 Watt floods once (~300W total) and had to upgrade to a 16C breaker. (Phew..that was too close for comfort on R1+R2 for my already installed cables..). I'd began with 6B and taken every step up from there till I arrived at 16C. - These were Meanwell drivers on Ledzip floods.
 
Hi - can you spell out the site Ze, the circuit design, cable sizes lengths and loads? I'll keep me devious thoughts to meself just now :) .
 
You could use thermistor in-rush current limiters as I have done but you have to work out its required cold resistance and power rating and then faff about mounting it inside an enclosure which takes into account it gets hot.

You'd be better off using one of these ready made devices which can solve LED problems like yours:

ESB 101-23 - Peak current limiter, 23 A, 2000 µF - https://www.reichelt.com/gb/en/peak-current-limiter-23-a-2000-f-esb-101-23-p167632.html?CTYPE=0&MWSTFREE=0&PROVID=2788&wt_guka=54950995355_263550067601&PROVID=2788&gclid=EAIaIQobChMI9-a2i8za3QIVr7ftCh24QQA7EAQYBSABEgKcYvD_BwE&&r=1
 
Update!!

It was definitely in rush current!

I have not experienced it being a problem before as I only do domestic and Type C breakers are rarely needed.

I had taken in to account VD, worked out what the Zs was likely to be and used 6mm SWA for the approx 100m run.

My Zs is 1.45ohms.

I am picking up a Type C 6A and 10A tomorrow and will try those, however I did have a 16A Type B and this is working fine. The max Zs for 16A Type B is 2.2 ohms so I have been saved.

I can run another circuit for the next 5 x 200W lights or I might find that a 20A type B works for all 10 lights as long as the Zs < 1.75ohms.

I'm embarrassed that I didn't factor inrush current in to my design, it's not acceptable to be acting reactively like this to a problem that should never have arisen!

One last question..

What is the relationship between Type B and Type C MCB's with regards inrush current? What I mean is if for example a 6A Type B could take perhaps 100A for 0.2s without tripping what would the equivalent be for a 6A Type C be? Is there some data sheets on this or some interesting reading somewhere?

ps.. these are the lights http://www.belllighting.co.uk/fittings/SkylineProLEDFloodlightsWallpacks

Apparently the inrush current is approx 75A.
 
Update!!

It was definitely in rush current!

I have not experienced it being a problem before as I only do domestic and Type C breakers are rarely needed.

I had taken in to account VD, worked out what the Zs was likely to be and used 6mm SWA for the approx 100m run.

My Zs is 1.45ohms.

I am picking up a Type C 6A and 10A tomorrow and will try those, however I did have a 16A Type B and this is working fine. The max Zs for 16A Type B is 2.2 ohms so I have been saved.

I can run another circuit for the next 5 x 200W lights or I might find that a 20A type B works for all 10 lights as long as the Zs < 1.75ohms.

I'm embarrassed that I didn't factor inrush current in to my design, it's not acceptable to be acting reactively like this to a problem that should never have arisen!

One last question..

What is the relationship between Type B and Type C MCB's with regards inrush current? What I mean is if for example a 6A Type B could take perhaps 100A for 0.2s without tripping what would the equivalent be for a 6A Type C be? Is there some data sheets on this or some interesting reading somewhere?

ps.. these are the lights http://www.belllighting.co.uk/fittings/SkylineProLEDFloodlightsWallpacks

Apparently the inrush current is approx 75A.
I had that problem once, inrush, you mucky people, some will get the joke some wont, not going to explain.
 
Not a cheap solution but if you had sequenced switching so that only three lights came on at any one time, with a 0.5s delay or so between each bank this would alleviate the inrush current problem. You could fit delay on relays set to different times for each light or I believe you can buy specific staged switching systems.
The thermistors are a problem because of the heat and they ought to be switched out after start up which is more expense and messing about.

The current difference between B and C (and D) is not something I have seen data on but logic indicates that if on heavy overload an MCB trips in 10 ms, then any current over the trip rating but faster than 10 ms will not give it time to trip. Therefore you need to slightly average the current seen on start up so if an LED has 150A for 0.3ms if may seem to the MCB to be only 50A (or less) over 10ms, in this case a B type would trip, a C type may well trip and a D type would not trip.
 
Glad you got it sorted out. Inrush current for switch mode power supplies / LED drivers is something that's not easy to calculate accurately. If you have a borderline case, which it sounds like yours was, whether it trips can actually boil down to how near the zero point the supply waveform happens to be when the switch closes and whether the lights have been recently run or not.
 
Just as a footnote, if you're planning to add more lights onto the same supply I'd suggest supplying them via a separate switch or timer or PIR or whatever switching system they're on, even if it works out more costly. That way they won't all switch simultaneously which would add to the inrush current issue.
 
Just as a footnote, if you're planning to add more lights onto the same supply I'd suggest supplying them via a separate switch or timer or PIR or whatever switching system they're on, even if it works out more costly. That way they won't all switch simultaneously which would add to the inrush current issue.
Thanks Marvo.
The plan is to have the next 5 on a separate switch.
I appreciate the detailed and informative responses, thanks again.
 
Well the 5 lights work fine on either a 10A Type B or a 6A Type C, so I should be ok with all 10 on a 20A Type B or possible a 10A Type C. Also the next 5 will be switched separately so that will avoid the inrush current of all 10 at the same time. Happy :)
 
Well the 5 lights work fine on either a 10A Type B or a 6A Type C, so I should be ok with all 10 on a 20A Type B or possible a 10A Type C. Also the next 5 will be switched separately so that will avoid the inrush current of all 10 at the same time. Happy :)
Until some body switches, all of the lights on at once, you just know it's going to happen Murphy's Law dictates this.
 
You can find the time Vs current curves for type b,c,d MCB in the installation and test regulations.
Type B instantaneous trip is 3-5 times rating
Type C instantaneous trip is 5-10 times rating
Type D instantaneous trip is 10-20 times rating

This is the magnetic trip and applies to inrush current.

I should add that the current is RMS current, so averaged over 1 half cycle. So very high inrush currents lasting less than half a cycle might not trip the MCB if the average over that cycle is lower than the trip characteristics.
 

Reply to Advice regarding inrush current please? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
966
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs). 6A breaker in Garage consumer...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock