Hi all,

We had a cable ran down to the bottom of our garden for when we were going to get a garage but we decided against it.

I was looking to get an outside socket fitted down there for hoovering the car etc.. the only problem is there isn't anywhere really to mount it. Currently the cable is just coming out of the ground. I was thinking maybe a concrete block or something but not sure on regulations etc..

Cheers
 
all depends on if you've got RCD protection on the cable or not. overcurrent device, size of cable etc. a concrete or timber stanchion would be best and an IP65 socket ( RCD socket if none at supply end )
 
It is rcd protected and the cable is shielded not sure of size though. If I could use a concrete post that would be ideal or even hide it into a statue or something
 
check the cable size. concrete post is ideal. if cable is 6mm, use a 32A MCB.../ 2.5mm, then a 20A MCB./ if 1.5mm, use a 10A. if you are using SWAarmour as cpc, then ensure the glanding and fly leads are sound and connected. obviously, you will test the install.
 

Reply to Advise for an outside socket in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
594
Hi there - good site. Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline)...
Replies
4
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
564

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock