Discuss AFDD - Has this left a loophole for landlords? in the UK Electrical Forum area at ElectriciansForums.net

Agree on comments the other thing that seems to be appearing is the actual faulty AFDD’S & actually knowing the fault especially on the combined RCBO/ AFDD.
I personally not fitted any yet & hopefully don’t have to
 
Surely, it is the owner's responsibility to ensure that the building complies with legislation, not the electrician's.
As long a you have a written statement in your contract as to the purpose and use of the building, you should be covered legally.
Having said that, if any client of mine tried this kind of tactic, be would no longer be my client.
 
Agree on comments the other thing that seems to be appearing is the actual faulty AFDD’S & actually knowing the fault especially on the combined RCBO/ AFDD.
I personally not fitted any yet & hopefully don’t have to
Yip, they're going to be a pain. Any I've seen so far have some method of indicating the reason for tripping though, but if it's a AFDD activation it's just as likely to be an appliance fault as an install fault.
 
Surely, it is the owner's responsibility to ensure that the building complies with legislation, not the electrician's.
As long a you have a written statement in your contract as to the purpose and use of the building, you should be covered legally.
Having said that, if any client of mine tried this kind of tactic, be would no longer be my client.
The thing is if something happens it comes down to a case of LL's word against the sparks word.

... LL tells spark it's a hostel - (no AFDD required), Spark issues EICR / EIC and off he goes.
.... LL produces 'Satisfactory' cert and gets HMO licence - (with no AFDD's fitted)
.... Something nasty happens and all goes bad. Investigation uncovers a cert for install that hasn't got AFDD's in a building used as an HMO
.... LL, to save his neck, says the spark said it was satisfactory and I took his word for it, he never told me I needed AFDD's and how else was I to know, that's why I got a spark to check out the wiring for me. I'm a responsible LL your Honour, I depended on the Spark to do his job right.
.... Spark says I was told it was a Hostel and did the inspection to the relevant standards in light of what I was told. How would I know a Hostel from an HMO?
.... LL - I said no such thing, just asked for a cert and got it, seems I got a cowboy spark!

It all gets into a nasty one word against the other and at best spark ends up with a very brused reputation by association and at worst.......

Surely this needs sorted out IET??
 
LL tells spark it's a hostel - (no AFDD required), Spark issues EICR / EIC and off he goes.
.... LL produces 'Satisfactory' cert and gets HMO licence - (with no AFDD's fitted)
.... Something nasty happens and all goes bad. Investigation uncovers a cert for install that hasn't got AFDD's in a building used as an HMO
.... LL, to save his neck, says the spark said it was satisfactory and I took his word for it, he never told me I needed AFDD's and how else was I to know, that's why I got a spark to check out the wiring for me. I'm a responsible LL your Honour, I depended on the Spark to do his job right.
.... Spark says I was told it was a Hostel and did the inspection to the relevant standards in light of what I was told. How would I know a Hostel from an HMO?
.... LL - I said no such thing, just asked for a cert and got it, seems I got a cowboy spark!

It all gets into a nasty one word against the other and at best spark ends up with a very brused reputation by association and at worst.......
before the contract .
saying you have declined to have them installed .
you go by the regs not him .
 
The thing is if something happens it comes down to a case of LL's word against the sparks word.

... LL tells spark it's a hostel - (no AFDD required), Spark issues EICR / EIC and off he goes.
.... LL produces 'Satisfactory' cert and gets HMO licence - (with no AFDD's fitted)
.... Something nasty happens and all goes bad. Investigation uncovers a cert for install that hasn't got AFDD's in a building used as an HMO
.... LL, to save his neck, says the spark said it was satisfactory and I took his word for it, he never told me I needed AFDD's and how else was I to know, that's why I got a spark to check out the wiring for me. I'm a responsible LL your Honour, I depended on the Spark to do his job right.
.... Spark says I was told it was a Hostel and did the inspection to the relevant standards in light of what I was told. How would I know a Hostel from an HMO?
.... LL - I said no such thing, just asked for a cert and got it, seems I got a cowboy spark!

It all gets into a nasty one word against the other and at best spark ends up with a very brused reputation by association and at worst.......

Surely this needs sorted out IET??
Which is why I suggested you get in writing (and could also add a note on the EIC) confirming the type and usage of the building. Loophole closed.
 
HMO or Hostel; both would require local authority licensing, in which case I would speak with them FIRST and get it in writing where you would stand as the installer as you believe that LL has unscrupulous intentions.

If that licensing people say no AFFDs required then you are covered (as licensing conditions would be above 7671 [115.1])
 
Okay, just playing a bit of a devils advocate here but what if....

Spark sets out to do an HMO install for a regular LL, no formal contracts, has done lots of work for LL before, all done to the regs with AFDD's. Halfway through the job LL goes - 'what are those things at xx hundred / xx thousand pounds? I've never needed those before'. Spark explains now a legal requirement in an HMO. LL goes away fuming. LL turns up later and says 'I'm not paying for those take them out, it's a hostel not an HMO, don't need them'.

So, what's the chances of getting that in writing? - about zero.
What now ?
Walk away knowing you'll not get a penny for what you've done.
Put up and shut up.
Fit them anyway but only charge for RCBO's and take the hit.
Report to local authority - to which he'll deny all knowledge of the conversation.
I can't see any good option for a spark in this situation.

It just seems odd to me how an HMO has to have AFDD's and a Hostel doesn't when in the practical sense there is very little difference between them apart from the length of a guest / resident's stay. Surely the risk to life and property is similar in both and it would have been easy cover both in the regs.

As for some local authority inspectors picking up on it in the certs, any that I've seen wouldn't know an AFDD from a ciggy packet, all they look for is a big satisfactory or signature on the cert and they're content that someone else is carrying the can if it all goes south.

Like I said, just playing devils advocate here, thankfully I can walk away from this one with no loss, but sooner or later some poor sod is going to get caught out with this. I'm sure that any of us that do work for LL's know at least one or two who are as dodgey as heck.
 
HMO or Hostel; both would require local authority licensing, in which case I would speak with them FIRST and get it in writing where you would stand as the installer as you believe that LL has unscrupulous intentions.

If that licensing people say no AFFDs required then you are covered (as licensing conditions would be above 7671 [115.1])
In this case it's BS7671:2018 421.1.7 would take precedence over local authority requirements as it is a statutory requirement. I stand corrected on that point, still I'd rather work to a recognised standard than what someone in the local authority tells me.

421.1.7
Arc fault detection devices conforming to EN62606 shall be provided for
single phase AC final circuits supplying socket outlets with rated current
not exceeding 32A in:
• Higher risk residential buildings
• Houses of multiple occupancy (HMO)
• Purpose built student accommodation
• Care homes
NOTE 1: Higher Risk Residential Buildings are assumed to be residential
buildings over 18m in height or in excess of six storeys, whichever is met
fi rst. It is anticipated that in many areas, higher risk residential buildings
will be defined in legislation which can be subject to change over time,
as well as in risk management procedures adopted by fi re and rescue
services. Current legislation should be applied.
For all other premises, the use of AFDDs conforming to BS EN62606 is
recommended for single phase AC fi nal circuits supplying socket outlets
not exceeding 32A.

Where used, AFDDs shall be placed at the origin of the circuit to be protected
 
Last edited:

Reply to AFDD - Has this left a loophole for landlords? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I can't find any really up to date threads on whether we have to fit AFDD's. I am specifically talking about in a domestic premise. I can see...
Replies
42
Views
5K
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
36
Views
1K
My mate has family in Southern Ireland and he has been over there a couple of times this year helping them renovate a property. He has been...
Replies
14
Views
1K
We are new landlords and have just got an EICR done. The building is only 5 years old so I am shocked that remedial work has been noted as...
Replies
45
Views
11K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
745

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock