Discuss Agricultural rcd tt system pannel board. in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
22
Looking for recomendations for a pannel mccb board for a agricultural installation.
Looking at schnider or protuse (city own brand).
My understanding of 17th regs is as follows.
Tt with a rod / plate or tn as long as plate laid in floor, under concrete.

Then a 300ma s type main switch 4 pole. Do they do a main switch of this type or would it be mccb on final circuits with a rcd built in, but surely this would only be 3 pole.
Been genuine as I've never come across pannel boards with rcd protection before.
Any genuine help appreciated.
 
It is unusual to see 60947-2 devices with an integral rcd unit, you usually have to fit separate rcd modules. If you are considering this route you need to speak to Schneider or Eaton and they will design a bespoke panel. Hope Mr or Mrs Farmer have a large wallet.
 
Personally I would install a seperate RCD and enclosure before the MCCB board. I would do this for future maintenance that would allow the MCCB board to be safely isolated in its entirety. It would also afford additional protection to the supply as it enters the board.
 
The people you need to speak to are Schneider. The modules you fit are called vigi blocks which are an add on module to the mccb along with a neutral link block. Fitting these to a factory enclosure may require an extension chamber due to their size and if you have little or no experience with this you may experience some very expensive mistakes. Schneider will design a bespoke board for your needs and I would suggest following this route, it will not be like knocking up a consumer unit.
 
If you’re using the Powerpact panel board, you would have to use a VIGI module and a 4 pole MCCB instead of a main switch.
Acti 9, just use an RCCB instead of a main switch.
 

Reply to Agricultural rcd tt system pannel board. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
329
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
258
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
781
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock