Ok. Isolate again and remove the link you just put in. Then switch on.
Re#71 and the image of the ASHP control panel. There is a red light for the 'Programmer live'.
Could you observe and report its state (lit, not lit) when at the programmer you select HW constant and then select HW off at the programmer. I suspect the ASHP is in permanent HW priority mode irrespective of the state of the HW select button.
Re#71 and the image of the ASHP control panel. There is a red light for the 'Programmer live'.
Could you observe and report its state (lit, not lit) when at the programmer you select HW constant and then select HW off at the programmer. I suspect the ASHP is in permanent HW priority mode irrespective of the state of the HW select button.