Discuss All fuses blowing! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Proper Job

Hello
i have seen a first today.
i am working for a highway unit and have had to go and solve a fault .
I he I can explain this correctly as the wiring is in a bad state with a few under ground t joints to make it a bit more difficult for testing. So. The cable supplying the line of lights is a three phase cable with the yellow cable possibly being jointed under ground and going off to some lights that are not causing a problem. The cable continues on for about 150 meters. There are 8 lights within that 150 metres on the red and blue phase.the cables appear to loop in and out of the columns but may be jointed under ground, any thing is possible.and in the column is a mini is a double pole isolator and fuse carrier.
the problem is that at the last six columns each of the fuses have blown and I have yet to find out why.the main fuses feeding these circuits are ok. I have insulation resistance tested one of the cables from the column fuse to the light which turned out to be clear. I will test more tomorrow ,am sure it is something to do with the neutral being loose but would appreciate any advice.
thanks
 
Sounds like fun, not up on high way stuff but if it were me i'd look at the neutral too , any 3 phase line conductor normal 230 v between it and neutral shoots up to 400v if the neutral is not connected. Had rarther alot of super bright smoking lights when a neutral had been pulled out on a 3 phase comando plug one time.

Worst case just break it down ad check each bit of cable at a time.... ahhh the joys of fault finding.

Good luck
 
As well as r1 and r2 readings ,am I right in thinking that I should get the Rn readings also as they will tell me where the bad neutral is .
thanks again everyone for the help
 
On Friday I tested the three phase of that cable and every thing came back clear. The lowest ir reading of one of the phases was 8 meg ohms. I did r1 r. 2 readings and also r2 Rn and all readings were very healthy. As it was towards the end of the I just linked from one working light column to the drop feed of the first of the lights that is out and once I turned it on it blew the fuse.. Which is making me think that the last 6 lights have been damaged due to a surge or something, will test further when we I get back to that job, thanks for the advise about the loose neutral.
 
what sort of lanterns are they ?
the latest street lights have radio signal control for switching and also electronic dimming capability.
in other words there could be a group of lights , fitted from the same batch , that are duff.

you've proved that the underground swa is sound and the section fuses dont blow so i'd be looking closely at the lights.
do a IR test between LN&E to the t&e cable going up to each lantern , should show up any weak electronics
 
Last edited by a moderator:
I have done an ir test on each of the drops between l and earth then neutral earth. All came back clear.
how would test between live and neutral connected toghether tested to earth?
Cheers
 
doesnt matter as you've tested L & N to E earth separately so its done already.
seems a very strange fault i must say.
how long before the isolator fuses blow after changing them ?
a day ? a week ?
 
I would advise you check the control gear and photocell switch on each lantern. If these are old fittings that have not received correct maintenance there is a possibility that they may have moisture ingress or corrosion of the lamp internals. When you replace the fuses the photocells will kick in for a couple of mins which may be what induces the fault to the base of the columns hence blowing the fuses. An IR test may not highlight this as the fault is induced once the photocell operates.
 
Have you checked the voltage at each point L-N + L-E to see if your getting the right voltage.?
Assuming the fuses feed the lights at each column, could it be the lights/controls gear thats causing the problem and not the supply cable.
6 faulty lights does sound strange but do you know if they all blew at the same time or is it something thats occured over a long time and because 6 are now not working they are willing to spend some cash.
Good luck sounds a nightmare
 
Hi everyone .
I am not sure how old the lighting is but doesn't look old, it is part of the motor way so would take a long time to set up a lane closer to look at the heads,
I have hooked up test lamps at 5 of the 8 columns , and disconnected the cable drops from the faulty column lights. Power on and the test lamps work.
so I am now certain that it was the loose neutral on the three phase cable that has caused it
thanks again everyone and very good call on this one electric avenue
 

Reply to All fuses blowing! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
I am replacing some of the old receptacles in a 1940s house. Armored BX cable, two conductors, cable is the ground. Mostly pretty straightforward...
Replies
2
Views
344
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
996
I've been volunteering at my local village hall, installing audio and light systems. Converting what was originally an underused sports hall into...
Replies
68
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock