Discuss Aluminium Cables - Copper Busbar in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

ewatty

-
Reaction score
1
Hi All...

i have a little question...

We have Aluminium DC cables connecting onto Copper Busbars, but we car starting to get burning/galvanic oxidation. (the Large combiners are outside in metal cabinets so easily get moisture inside)

But some of it is due to the odd poor connection (lugs not tight enough on the cable or incorrect size of lug used) from install! But if i replace them, i want to do it right the first time.

I have looked at using bi-metal lugs, but they are stupidly expensive!

If i was to use a Aluminium Lug, with Anti-Corrosive Zinc Paste between it and the copper Busbar and stainless steel Bolts/locking washers will this help stop the corrosion? Due to the high DC voltage every connection has to be perfect!

Any thoughts?

thank you!
 
I'd use normal copper lugs that are coated.
 
What DC voltages / currents are you dealing with and what sized aluminum cables? I know bi-metal lugs are expensive but how many are you talking about? You can also use a cupal washer between the aluminium lug and the copper bar but they're also not cheap so antioxidant paste might be preferable on the contact faces.
 

Reply to Aluminium Cables - Copper Busbar in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Morning! Going to be working near the coast and will need to fit earth bonding outside. I originally chose stainless lugs to bond the copper...
Replies
7
Views
668
Hi I have been in the electrical contracting industry all my working life 40 years and became a member of the NICEIC in 2006. During this time I...
Replies
17
Views
2K
I'm doing another EICR, I still don't like doing them, and still seem to attract the weird/unusual/uncommon stuff. This time I'm faced with...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock