Discuss Amendment 2 coming out next year thoughts? in the UK Electrical Forum area at ElectriciansForums.net

Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,173
Just been reading an article regards Amendment 2 coming out next year.
The requirements for AFDD is going to create some interesting conversations with customers as they are not cheap. Unless manufacturers get their act together I would be surprised if in 12 months they have stock or are sensibly priced.
Its hard enough to get a consumer unit or RCBO at the moment,

 
Tell you what most of the 16th edition boards i come across are installed a lot better than most metal clad amd3 boards!
Love the old plastic 16th ed board, you could neatly butt MT mini trunking up to it really neatly Using the specially designed square cut-outs...
 
Just been reading an article regards Amendment 2 coming out next year.
The requirements for AFDD is going to create some interesting conversations with customers as they are not cheap. Unless manufacturers get their act together I would be surprised if in 12 months they have stock or are sensibly priced.
Its hard enough to get a consumer unit or RCBO at the moment,

has this been confirmed now then?
 
When paragraph 3 states
As with all Amendments to BS 7671, itā€™s only when all of the comments that were received during the DPC period have been reviewed and considered that the final version of BS 7671 Amendment 2 is issued. As such, some of the proposed changes weā€™re discussing may or may not come into force.
What is the point of the article unless it is to condition us for the inevitable

If all the proposals go through it will do nothing to improve safety as it will price people out of updating / upgrading their electrical installation
 
It'll just give rise to more dodgy DIY electrical bodging and unofficial cash in hand work due to affordability.
But the IET powers that be who also have big interests in manufacturing will want their AFDD development costs back.
 
DId I read on here not too long ago that in the US, it is not uncommon to fit AFDDs (or whatever they call them over there) on some circuits, but then remove them after sign-off of the work because of nuisance tripping? Or am I imagining this?
 
If the afdd reg comes in then that extra.socket for mrs jones has just become Ā£150 more expensive as you would need to price one of these in. Assuming you can get one. Then if there are issues in the circuits try and find it! Joy of joy you could be there 2 days adding a socket.
I guarantee though the drove by eicr brigade will love this and use it to mark otherwise sound installs as unsatisfactory and immediately tell people they must have afdds. Some landlords are going to be fleeced when this does eventually come in.!
Bit like the changes in amd3 which consumer units. How often do we see on the forum some landlord asking about a cheap EICR being unsatisfactory due to plastic board when everything.else is pretty much okay.
 
When paragraph 3 states

What is the point of the article unless it is to condition us for the inevitable

If all the proposals go through it will do nothing to improve safety as it will price people out of updating / upgrading their electrical installation
Totally correct it will now have the opposite effect
How many more add ons do we have to keep up selling to the customer constantly

I (like a lot of others)do a lot of domestic minor works and existing circuit alterations

This will be an absolute nightmare in regards to availability of devices and compatibility with existing brands of consumer units
 
Apart from the fiasco that will become foundation earthing, my largest consideration with AFDD's is simply how the heck are we meant to test them. I can see it now that the likes of Megger and Fluke et al are rubbing their hands in glee knowing that soon they'll be selling thousands and thousands of new MFT's......
 
OK.... results of some brief research is that basically they can't be tested anyway, beyond the internal T button (am sure this must have been discussed in other threads on here in the past). What WILL be a pain for testing is that you can't do a 500V IR from source side due to the internal electronics so gone are the days of a global IR at the board, each leg needs removing.
 
Arc Fault Circuit Devices can;t be tested beyond the T button and if they won't hold in then bin it and buy a new one.
 
Apart from the fiasco that will become foundation earthing, my largest consideration with AFDD's is simply how the heck are we meant to test them. I can see it now that the likes of Megger and Fluke et al are rubbing their hands in glee knowing that soon they'll be selling thousands and thousands of new MFT's......
Had a conversation with a couple of guys on the Megger stand at an Elex a couple of years ago when the AFDD's started appearing and they were saying that it was unlikely that there would be a tester available to confirm the operation of AFDD's. The identification of nuisance tripping came into the conversation and the conclusion was you swap it out and if it stops the tripping then it was faulty if not you are looking for a fault on the circuit that may not be found with the test equipment we have and possibly the only way to cost effectively repair would be to rewire the whole circuit
 
DId I read on here not too long ago that in the US, it is not uncommon to fit AFDDs (or whatever they call them over there) on some circuits, but then remove them after sign-off of the work because of nuisance tripping? Or am I imagining this?
No I am pretty sure it was @Megawatt
 
This D.S vid on Affddds is probably the best explanation of how an Afffdddds work on the web

Great video!

Dreading the thought of starting to install and fault find these when they become required, at least an RCD fault you have a means to test and narrow it down, seems its just a visual inspection is all we can really do in some cases and if no scorch marks are apparent just retighten connections and keep resetting the thing till its happy

Even IR testing will only really work on a parallel fault

Definatly sounds like a good idea with electric shower circuits though

Can see alot of sparkys ducking out of these types of call out in the future
 
Great video!

Dreading the thought of starting to install and fault find these when they become required, at least an RCD fault you have a means to test and narrow it down, seems its just a visual inspection is all we can really do in some cases and if no scorch marks are apparent just retighten connections and keep resetting the thing till its happy

Even IR testing will only really work on a parallel fault

Definatly sounds like a good idea with electric shower circuits though

Can see alot of sparkys ducking out of these types of call out in the future
Half day call-out , drop off every single point and check every single connection.
 
My favorite proposed change along with the AFDD thing is earth of building foundations, who the hell is going to know once the concrete is poured, and how do you check it after for an EICR!
Oddly enough that is the one change that I think makes sense!
  • AFDD - too expensive, little proof they actually are value for money in terms of saved lives versus lives lost due to board changes being refused on cost, etc.
  • RCD mandatory - stupid for data centres and the like where you have high leakage stuff, safe environment, and want to be able to swap in an emergency without getting a spark in some time next week.
  • Foundation earth for TN-C-S - should have been in the regs years ago when it started!
As for testing a foundation earth, my suggested approach is two bond wires to the buried steel in separate locations then to verify the bond soundness you do an end-end check on the two bond wires, like the RFC test.
 
@pc1966 I agree that it is a perfectly reasonable idea and that done correctly would be of benefit! Having been involved with agricultural installations for several years this is normal practice and if done as you say can be easily confirmed that it is still connected correctly. If you can find a trustworthy groundwork team! I have been on some jobs where it has been completely forgotten and has caused some major works to rectify.
 
OK.... results of some brief research is that basically they can't be tested anyway, beyond the internal T button (am sure this must have been discussed in other threads on here in the past). What WILL be a pain for testing is that you can't do a 500V IR from source side due to the internal electronics so gone are the days of a global IR at the board, each leg needs removing.
I dunno @dseselectric did a rather spiffing video on an AFDD tester ?
 
Could you not test an afdd by getting two loose wires then using some vde pliers create pretty little arcs..??
In real terms a sort of tazer like device with the arc in an enclosure?
youse got shares in knipex/CK/bahco?
 
my tuppence worth. those of us who are bona fide sparks will ignore the afdi crap and still do a decent safe job at a sensible cost, thus doing our best to keep the cowboys at bay.
 

Reply to Amendment 2 coming out next year thoughts? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Got my 18th Ed certificate late last year, now doing 2391. Obviously Amendment 2 has come out since then, and I see these courses available to...
Replies
113
Views
8K
Good Evening, Amendment 2. Just wanted to ask your thoughts on this once more money making criteria that's been laid before us? The Introduction...
Replies
16
Views
2K
Conversation developed with a middle aged lady who has recently lost her husband. Note to self, stop walking dog around the graveyard Anyway...
Replies
5
Views
1K
Interesting situation has come up. I have a client who rents out portable toilets - higher end ones with proper flushing toilets/urinals that are...
Replies
7
Views
3K
  • Locked
DIY Looking for DIY Advice on ElectriciansForums.net - Also, we're looking for professional electricians to help out in there. I know this is a...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock