Discuss Amendment 3 2-module enclosure or 100A DP isolator. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
113
I have a situation where I have fitted an RCD incomer consumer unit alongside another existing RCD incomer unit to provide RCD protection for remaining circuits. I didn't fit an isolator for the two units so to turn off all power to the building you have to turn off both RCDs. I know there was a thread on here a few weeks ago about whether or not this is compliant and somone (I forget who, sorry!) posted a link to a NAPIT document that advised that this is compliant as the consumer units with their associated circuits can be regarded as separate installations. Anyway the customer now wants me to refit the old main switch from the previous MEM 3 unit I replaced (impractical and bad idea for so many reasons) in order to provide a single point of isolation (to paraphrase!). I'd like to offer to fit a new isolator (I even have a few nocking around), but I can't find an amendment 3 2-module enclosure for sale anywhere, or indeed an amendment 3 100A DP isolator - they all seem to be plastic. Anyone know of any?
 
I have a situation where I have fitted an RCD incomer consumer unit alongside another existing RCD incomer unit to provide RCD protection for remaining circuits. I didn't fit an isolator for the two units so to turn off all power to the building you have to turn off both RCDs. I know there was a thread on here a few weeks ago about whether or not this is compliant and somone (I forget who, sorry!) posted a link to a NAPIT document that advised that this is compliant as the consumer units with their associated circuits can be regarded as separate installations. Anyway the customer now wants me to refit the old main switch from the previous MEM 3 unit I replaced (impractical and bad idea for so many reasons) in order to provide a single point of isolation (to paraphrase!). I'd like to offer to fit a new isolator (I even have a few nocking around), but I can't find an amendment 3 2-module enclosure for sale anywhere, or indeed an amendment 3 100A DP isolator - they all seem to be plastic. Anyone know of any?

Try this.

HAGER 100 AMP MAIN ISOLATOR DOUBLE POLE + METAL ENCLOSURE (MS) | eBay - http://m.ebay.co.uk/itm/HAGER-100-AMP-MAIN-ISOLATOR-DOUBLE-POLE-METAL-ENCLOSURE-MS-/112086514879
 
You want a metal enclosure with din rail and door - will this work?
British General 5-Module 3-Way Populated Garage Consumer Unit - http://www.NoLinkingToThis/p/british-general-5-module-3-way-populated-garage-consumer-unit/1926g
 
Last edited:
I got the part number from Wylex NSPE 7500. Can't find much info on it when googling it. Got sent a pic from my wholesaler. Apparently the newer version is about two inch longer so more room at the bottom of the isolator.

IMG_0417.JPG
 
I recently got an isolator fitted by my DNO in my house - they supplied a Wylex unit in a plastic enclosure and this was less than a month ago. So have they breached the regs?

This is it -

iso.jpg
 
no they don't work to bs7671 plus there is argument that a double pole switch doesn't fall foul of 421.1.201. I would seek clarify from your CPS on this though.
FWIW - In general conversation with Assessor - plastic may be ok in a meter box that is in/on an external wall facing out, but it's not ok if used inside. This implied (to me) Assessor considered it to be affected by the full metal jacket reg.
 
Any din rail mounted isolator will fit a standard DIN rail they are all designed to align at the same height, the problem comes when you want the terminals to align with a busbar, since you have tails to fit there should be no problem.
Since you have the four module enclosure you could even fuse it down with a fuse carrier as well! (Though I do not see any point in doing that)
 
Any din rail mounted isolator will fit a standard DIN rail they are all designed to align at the same height, the problem comes when you want the terminals to align with a busbar, since you have tails to fit there should be no problem.

Thought as much but wanted to be sure :). Thanks for confirming!

Since you have the four module enclosure you could even fuse it down with a fuse carrier as well! (Though I do not see any point in doing that)

Yes no need - smallest tails present are 16mm2 and the cutout is 60A. I would have bought a two module but they just have 20mm knockouts - no good for tails!
 

Reply to Amendment 3 2-module enclosure or 100A DP isolator. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock