Doing a EICR in a college…there have been many over the years, it’s approximately 50 years old & improvement happens every so often.
The new amendment concerning all areas of the installation on support of cables to prevent premature collapse.
This college consists of plastic containment throughout its corridors & on fire exit routes.
My opinion on this maybe a recommendation C3… & noted to whom concerned, this would require major works throughout.
Some of this containment is above false suspended ceilings, most clipped direct to the concrete floor of the above floor & visible, any advice much appreciated
 
Agree, nothing mentioned in any other EICR’s either, about the supports, but with all the news on the cable containment, should this now be noted…
 
Have you actually checked the plastic containment doesn't have metal clips fitted internally throughout or is the best way forward to put it down as a limitation and as such not verified
A C3 code could leave you looking a bit daft if you haven't verified it throughout and to do that could be very time consuming
 
Agree, nothing mentioned in any other EICR’s either, about the supports, but with all the news on the cable containment, should this now be noted…
It isn't news it needs noting. I tend to take a sample inspection on a site just to check because as above you can't always see it.
 
Have you actually checked the plastic containment doesn't have metal clips fitted internally throughout or is the best way forward to put it down as a limitation and as such not verified
A C3 code could leave you looking a bit daft if you haven't verified it throughout and to do that could be very time consuming
It’s definitely not compliant
 
Yes its been up for @ least 15 years…
So you are making an assumption on the age of the installation and haven't removed all the containment lids to verify it as it would take a lot of time and risk damaging the plastic containment which often becomes brittle as it ages
 
So you are making an assumption on the age of the installation and haven't removed all the containment lids to verify it as it would take a lot of time and risk damaging the plastic containment which often becomes brittle as it ages
The college was built in the 60’s, the plastic trunking was fixed to the concrete ceilings, this trunking & plastic conduits are seen in all corridors on 1st floor up to the 3rd floors, & also on fire exit routes from corridors to staircase.
Several EICR have been performed in the years, no mention of this, seeing the importance of premature collapse of wiring systems, what would be the correct assumption to make.
My opinion would be a note & a classification code would maybe Code 2
 

Reply to Amendment now problems later in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
78K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock