Hi.

excuse my ignorance. I have seen this before. Why is the phase in this picture taken through two of the poles in this manner?

the isolator is wired in exactly the same way with the phase going through line contact out the top and back through another pole.

what am i missing please?

thanks

john
 
Hi.

excuse my ignorance. I have seen this before. Why is the phase in this picture taken through two of the poles in this manner?

the isolator is wired in exactly the same way with the phase going through line contact out the top and back through another pole.

what am i missing please?

thanks

john
You might have forgotten to add the picture.
 
Without the pic' as expressed it might be difficult to respond although if we are talking about a 3 pole contactor with overload then it may be the overload monitors 3 poles and has balance and/or loss protection so in the case of single phase you have line and neutral and an empty pole, looping the line gives an output on each pole for the overload to recognise...... if it's not this then need that pic.
 
Without the pic' as expressed it might be difficult to respond although if we are talking about a 3 pole contactor with overload then it may be the overload monitors 3 poles and has balance and/or loss protection so in the case of single phase you have line and neutral and an empty pole, looping the line gives an output on each pole for the overload to recognise...... if it's not this then need that pic.
Ohhhh bugggah. Sorry. Attached now
 

Attachments

  • EEEF147B-FB45-4CF4-9A57-97F1DFDBE3C4.jpeg
    351.5 KB · Views: 22
Without details of the actual breaker we cannot be sure but most 3ph mcb's do not give balance monitoring so this is purely for redundancy, they could have easily just fitted a 2 pole option here, however if the breaker has phase loss monitoring then that is why, the schematic symbol used in each pole does not suggest that is the case so I think it is just convenient redundancy or the designer doesn't fully understand the functional concept of a MCB.
 
Without details of the actual breaker we cannot be sure but most 3ph mcb's do not give balance monitoring so this is purely for redundancy, they could have easily just fitted a 2 pole option here, however if the breaker has phase loss monitoring then that is why, the schematic symbol used in each pole does not suggest that is the case so I think it is just convenient redundancy or the designer doesn't fully understand the functional concept of a MCB.
Agreed - strikes me that it's not an MCB but just an isolator, though why you'd spec a 3p when a standard 2p would do it beats me.
 
Without details of the actual breaker we cannot be sure but most 3ph mcb's do not give balance monitoring so this is purely for redundancy, they could have easily just fitted a 2 pole option here, however if the breaker has phase loss monitoring then that is why, the schematic symbol used in each pole does not suggest that is the case so I think it is just convenient redundancy or the designer doesn't fully understand the functional concept of a MCB.
Thanks for the comment. It is single phase. And why did the installer fo the sane in the 3 pole isolatet located a few feet away?
877828BA-64EC-4406-9CD3-E12117E7F22B.jpeg
 
Our replies would be better if the schematic reflected the actual install, that is not a circuit breaker as denoted on the schematic, that is an isolator, having said that if the cover is yellow it will denote it is for emergency isolation, in said cases where possible it is good practice to utilise spare poles for redundancy in these circumstances but it shows poor initial design if deliberately done in design, many of these isolators are off the shelf and they tend to stock 3 or 4 pole so purchase convenience is often the reason we have spare poles.
Without seeing the whole schematic or down stream devices I cannot comment on whether the isolator should actually be a circuit breaker in this case.
 
Our replies would be better if the schematic reflected the actual install, that is not a circuit breaker as denoted on the schematic, that is an isolator, having said that if the cover is yellow it will denote it is for emergency isolation, in said cases where possible it is good practice to utilise spare poles for redundancy in these circumstances but it shows poor initial design if deliberately done in design, many of these isolators are off the shelf and they tend to stock 3 or 4 pole so purchase convenience is often the reason we have spare poles.
Without seeing the whole schematic or down stream devices I cannot comment on whether the isolator should actually be a circuit breaker in this case.
I think there’s so many variations on symbols for switches/isolators it’s hard to make that distinction?
 
It is often easier to get SP or 3P MCBs than DP, so there might be a reason for use 3P as "standard" but I don't see much reason for wiring that way.

Where you sometimes see a 3P breakers or switches series-wired is for DC systems to increase the breaking limit where there is no zero-crossing of AC current to help extinguish the arc, though that is something to check with the manufacturer that it is acceptable.
 
I think there’s so many variations on symbols for switches/isolators it’s hard to make that distinction?
The symbols we use in schematics are of a few international standards, recognising what the symbol is here is a circuit breaker with only overload protection and no magnetic trip, the partial box shape on the line designates overload protection, if it was accompanied by a dome shape then we would have a standard thermo/magnetic circuit breaker which we use as a standard to protect circuits across the industry. (like your standard mcb)
A switch isolator is a different symbol altogether and I suspect the schematic designer has limited understanding here of the correct symbols to use, the relevant standards here are either ANSI (American) or EIC which is mostly the rest of the world, but the differences are not that big.

I have to agree though, I have seen some very inventive versions of symbols and clearly incorrectly applied symbols in my time.

@John- All the information for that schematic should be included on the schematic or a ref' code/symbol should be attached with a key elsewhere to denote its ratings etc Q would be a recognised standard marker for this schematic device followed by a number to identify it against others in use so if its the primary device it would be Q1 and you schematic key would identify its ratings. Just looking at the fact it has been built up out of 3 single overload devices then boxed and no common switching link I thus conclude it has been drafted by someone who clearly doesn't know the standards or hasn't got the software to do a professional draft.
 
Last edited:

Reply to Another genset question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
844
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
864
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock