Discuss 3-Way Switch Loop, Ceiling Fed Multi-fixture Wiring Puzzle - Need Help in the UK Electrical Forum area at ElectriciansForums.net

NNMark

DIY
Reaction score
0
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed ground wires as one of the switch leg/loop travelers on a 3-way. Obviously, this is completely wrong and a fire hazard, so I decided to try to rework the mess, and ended up with a big headache.

Here's my question - can you help with this wiring puzzle?

Is it possible to wire this configuration with only two 12-2 between the two ceiling fixtures? I believe it takes five wires (not four) and that's why wiring was done improperly using a ground wire.

Here's a summary of the circuit (see attached picture):
  • Two ceiling boxes (1A + 1B) controlled by two 3-way switches (1A + 1B).
  • Power enters the ceiling box 1B with 12-2 cable
  • Switch 1A is connected Ceiling Box 1A with 14-3 cable
  • Switch 1B is connected Ceiling Box 1B with 14-3 cable
  • Ceiling box 1A and 1B are connected with two 12-2 cables
  • Ceiling box 1A also houses two additional 12-2 cables to power another ceiling fixture #2 with a single pole switch #2 loop.
So the issue is uninterrupted power needs to travel from Ceiling box 1B to Ceiling Box 1A in order to feed Ceiling fixtures #2. AND, the 3-way switch travelers need to also pass between ceiling boxes 1A and 1B to control both fixtures 1A and 1B.

See attached photo.

Am I missing something, is there another way to wire the circuit? I believe I'm one wire short between ceiling box 1A and 1B -- 5 wires are required not 4.

My backup plan is to simply replace the 3-way switches with single poles switch loops and control lights 1A and 1B separate. But, before I go this route, I thought I would see if anyone can solve this wiring puzzle.

Thank you in advance.
-NNMark
IMG_1588.jpeg
 
Last edited by a moderator:
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed ground wires as one of the switch leg/loop travelers on a 3-way. Obviously, this is completely wrong and a fire hazard, so I decided to try to rework the mess, and ended up with a big headache.

Here's my question - can you help with this wiring puzzle?

Is it possible to wire this configuration with only two 12-2 between the two ceiling fixtures? I believe it takes five wires (not four) and that's why wiring was done improperly using a ground wire.

Here's a summary of the circuit (see attached picture):
  • Two ceiling boxes (1A + 1B) controlled by two 3-way switches (1A + 1B).
  • Power enters the ceiling box 1B with 12-2 cable
  • Switch 1A is connected Ceiling Box 1A with 14-3 cable
  • Switch 1B is connected Ceiling Box 1B with 14-3 cable
  • Ceiling box 1A and 1B are connected with two 12-2 cables
  • Ceiling box 1A also houses two additional 12-2 cables to power another ceiling fixture #2 with a single pole switch #2 loop.
So the issue is uninterrupted power needs to travel from Ceiling box 1B to Ceiling Box 1A in order to feed Ceiling fixtures #2. AND, the 3-way switch travelers need to also pass between ceiling boxes 1A and 1B to control both fixtures 1A and 1B.

See attached photo.

Am I missing something, is there another way to wire the circuit? I believe I'm one wire short between ceiling box 1A and 1B -- 5 wires are required not 4.

My backup plan is to simply replace the 3-way switches with single poles switch loops and control lights 1A and 1B separate. But, before I go this route, I thought I would see if anyone can solve this wiring puzzle.

Thank you in advance.
-NNMarkView attachment 110240
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed ground wires as one of the switch leg/loop travelers on a 3-way. Obviously, this is completely wrong and a fire hazard, so I decided to try to rework the mess, and ended up with a big headache.

Here's my question - can you help with this wiring puzzle?

Is it possible to wire this configuration with only two 12-2 between the two ceiling fixtures? I believe it takes five wires (not four) and that's why wiring was done improperly using a ground wire.

Here's a summary of the circuit (see attached picture):
  • Two ceiling boxes (1A + 1B) controlled by two 3-way switches (1A + 1B).
  • Power enters the ceiling box 1B with 12-2 cable
  • Switch 1A is connected Ceiling Box 1A with 14-3 cable
  • Switch 1B is connected Ceiling Box 1B with 14-3 cable
  • Ceiling box 1A and 1B are connected with two 12-2 cables
  • Ceiling box 1A also houses two additional 12-2 cables to power another ceiling fixture #2 with a single pole switch #2 loop.
So the issue is uninterrupted power needs to travel from Ceiling box 1B to Ceiling Box 1A in order to feed Ceiling fixtures #2. AND, the 3-way switch travelers need to also pass between ceiling boxes 1A and 1B to control both fixtures 1A and 1B.

See attached photo.

Am I missing something, is there another way to wire the circuit? I believe I'm one wire short between ceiling box 1A and 1B -- 5 wires are required not 4.

My backup plan is to simply replace the 3-way switches with single poles switch loops and control lights 1A and 1B separate. But, before I go this route, I thought I would see if anyone can solve this wiring puzzle.

Thank you in advance.
-NNMarkView attachment 110240

Hopefully you've sorted this by now, but for future readers I'll respond anyway. There is no way to properly operate this unless as you suggested, a 3-wire cable replaces the 2-wire cable between light 1A and light 1B. You would have to have a hot, a neutral, 2 travelers, and a switched leg. (Grounds not counted.) That's 5 conductors, and you have only 4.
 

Reply to 3-Way Switch Loop, Ceiling Fed Multi-fixture Wiring Puzzle - Need Help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

FYI --- This is a U.S. installation. I'm replacing a three way switch (the UK might more sensibly call it a two way switch??) with a Kasa Smart...
Replies
4
Views
775
I took a light down to put up a new fixture and now the light goes on but the switch doesn’t shut the light off. The power only stays on so I am...
Replies
3
Views
2K
Hello Forum! The building I maintain has some fluoro fixtures with battery backup ballasts. There is a 3-way switch at each end of the hallway...
Replies
1
Views
633
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
431
Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock