Discuss Another tripping rcd..... in the UK Electrical Forum area at ElectriciansForums.net

polo1

-
Arms
Reaction score
633
In case I've missed something- 40a mcb in an old Simplex cu feeding a standalone, plastic cu consisting of a 63a, 30ma rcd as main switch and a 40a mcb. 10mm t&e serving a 9.5 kw Mira shower via a 45a dp switch.
Random tripping of the rcd when the shower is off ( power to the switch internal to the shower, but shower not running).

Rcd ramps at 22ma, x1 & x5 results fine, Zs what you would expect with measured Zdb and length of cable. Insulation resistance 999 on all combinations and resistance of heating tank fine. All connections tight. Cable run in loft is visible, no damage.

I wasn't able to ir test N-E on remaing circuits due to not being able to isolate on this first visit (am going back when house is unoccupied) but any thoughts meantime??
 
Is there any water dripping /spraying inside the shower cover?

Nope, totally dry. Ran the shower for a good 15 mns. No signs of water ingress or leak at inlet.

Interesting point about dodgy neons; shower has two neon, these are only on when the shower is actually running. The 45a switch has one neon, and the switch is typically left in the on position.
 
It could,but the reason would may be apparent, if the lids have been off.

I take it the Simplex has no RCD? What bonding is present,are the other supplied accessories in the bathroom supplied from the non-RCD DB,such as lights,immersion,etc, are there sections of pipework separated by plastic... lots of opportunities for other electrical shananagins :)
 
Have you tried tapping (gently) on the side of the RCD to see if it trips as it may be just so worn that any vibration can cause a trip. 22mA on a ramp test is a bit low (passes but a bit low) so may indicate ease of switching, perhaps?
 
All, thanks for the responses.
Simplex board has no rcd; all other circuits off this board. Main & equipotential bonding is in place. Ramp test result in op.
Peg, all appears to be copper piping with no plastic connections/inserts.
And yes Richard, I did try tapping on the rcd - I learned that "trick" a good few years ago!
 

Reply to Another tripping rcd..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
885
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock