Discuss RCD trip without appliance powering on in the UK Electrical Forum area at ElectriciansForums.net

Markbebbs

DIY
Reaction score
0
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault:

I have a new kitchen fitted and two existing ovens connected to existing Cooker circuit. Both ovens have been working fine.

new 7.4kw hob has been just been fitted to replace a small 13a one and it’s been put on its own circuit.

If the cooker MCB is on, the RCD trips as soon as Hob MCB is switched on. If the cooker MCB is off and the hob MCB is on, RCD stays on. Hob works fine if cooker MCB is off.

Wondering if this could be a faulty RCD although I hear that’s pretty rare. CU is about 25 years old. RCD is hager u762 20470.

Thanks
 
It's unlikely to be a faulty RCD.
If CU is 25 years old I'm guessing there is only one RCD protecting half of it? A photo of the consumer unit would help.

It is possibly that the hob is RCD protected and the oven isn't, and there is some interconnection between the circuits.
 
It's unlikely to be a faulty RCD.
If CU is 25 years old I'm guessing there is only one RCD protecting half of it? A photo of the consumer unit would help.

It is possibly that the hob is RCD protected and the oven isn't, and there is some interconnection between the circuits.
Hi Tim

There is only 1 RCD on the CU. Hob doesn’t have its own. Seems the hob has been temporarily connected to an old unused shower circuit, which I have been told will be replaced with a smaller 32a MCB by the kitchen guys. It’s only been connected to test the hob because it was bought as ex display, not new.
 

Attachments

  • IMG_2484.jpeg
    293 KB · Views: 38
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault:

I have a new kitchen fitted and two existing ovens connected to existing Cooker circuit. Both ovens have been working fine.

new 7.4kw hob has been just been fitted to replace a small 13a one and it’s been put on its own circuit.

If the cooker MCB is on, the RCD trips as soon as Hob MCB is switched on. If the cooker MCB is off and the hob MCB is on, RCD stays on. Hob works fine if cooker MCB is off.

Wondering if this could be a faulty RCD although I hear that’s pretty rare. CU is about 25 years old. RCD is hager u762 20470.

Thanks
I read about earth leaks so unplugged some appliances - kettle, toaster, washing machine and the RCD isn’t tripping with oven and hob MCB’s on. Would this mean I should be talking to an electrician about either new CU or getting an additional RCD fitted?

Thanks
 
Cumulative leakage from several faulty appliances, which on their own don't trip the RCD, but added together might?

You would be better off having individual RCD protection for each circuit, i.e. a new all-RCBO consumer unit, rather than trying to add a second RCD. So don't have anyone suggest to fit a dual-RCD consumer unit.
 
I read about earth leaks so unplugged some appliances - kettle, toaster, washing machine and the RCD isn’t tripping with oven and hob MCB’s on. Would this mean I should be talking to an electrician about either new CU or getting an additional RCD fitted?

Thanks
Some testing is needed to verify the new circuit is correctly installed, and to find out which appliances are faulty.
It should be possible to get your current setup working. In due course, as suggested above, an RCBO board would allow 30ma leakage per circuit as opposed to 30ma for half the house.
Something like a Fusebox board with RTAM RCBOs that switch both live and neutral.
 
Have you had new circuits for sockets or have the sockets been extended from existing install, either way RCD will need upgrading to a Type A and if your new cooker \ hob has been installed with new cable from CU then will need protection....looking at the board i would say it needs some remedial work carried out for the new kitchen to conform to regs
 

Reply to RCD trip without appliance powering on in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
240
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
638
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
802
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock