Discuss Anybody familiar with this sign on a tester. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
It showing a “noise” sign when live testing sockets for some reason. Sometimes it does it and sometimes it doesn’t just think it’s weird.

Never knew tester could pick up signals from cables

FA20882B-195A-4752-A1E3-F98F11C07EC3.jpeg
 
Yes electrical noise can affect results when using low-current anti-trip test methods, if it displays this symbol you should use the high current test instead as the results may be incorrect.

It’s all in the manual for the tester:
DB978A54-5DB7-46FF-ADF6-E930D93C54D9.png
 
It usually comes up on low current ZS testing when other circuits are drawing a load shared by the same rcd.
Yes it’s very annoying.
 

Reply to Anybody familiar with this sign on a tester. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
539
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
750
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
286
Hope this is the right place to post! My old Megger 1710 MFT tester has a problem on the features button sometimes when selecting the Zs mode it...
Replies
1
Views
2K
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
12
Views
586

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock