Discuss Anyone fill the gavity where the tails enter in the UK Electrical Forum area at ElectriciansForums.net

S

scooterboy

Hi all, I had my assessment the other day and shown him a job with a replacement board. The tails ran up in the cavity wall from the meter box below on the outside of the house and in from the back of the cu, he said that I should seal the hole in the wall where the tails come through into the cu and inside the meter box where they enter the cavity. I've looked through the regs book and can't find it any where, thanks in advance, scooterboy
 
Did he not tell you why, if someone is to pull you up on something they should give you a reason.
 
Maybe he is allergic to these
full
 
Why not, I would and do. Just because it was suggested to you as, perhaps good quality work, you won't find everything in BS7671.

Incidentally, don't like running tails up cavity walls, if I can help it. :)
 
I would say this was applying sealing of penetrations against water ingress as required under the building regulations AD C ( and possibly fire under AD B). However if the tails were inside the meter cabinet then there would be little risk of water entry.
I would usually seal an opening in a wall if I can get to it.
Interestingly I am going to inspect a house today after a fire where the fire only penetrated the wall cavity from next door and apparently caused significant damage.
 
Stop the drafts so the householder is not tempted to seal with something unsuitable, like thermal insulation, that could cause the tails to overheat. Just a thought (and one I tend to act on).
 

Reply to Anyone fill the gavity where the tails enter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
402
Hi, Just had a new Smart Meter fitted yesterday along with isolator. The chaps installing the SMART meter used 16mm tails from the main DNO fuse...
Replies
16
Views
8K
Hi everyone, i might be having to run new meter tails from meter box to consumer unit which is just under 3m run, i have used 25mm 3 core before...
Replies
6
Views
3K
This is my first post and I hope I explain it correctly/ Simply. 1100sq foot single family home, 100 amp service. I am having an electrician...
Replies
2
Views
888
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock