Discuss Applying the 3 meter rule. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi. I am an recently retired industrial electrician, I am worried about an installation in my own home I did about 30 years ago. I supplied my burglar alarm control box. By Spuring off my ring main (unfused) about 4 feet to the alarm box. I may also have down sized the cable to 1.5mm T&E. I did not fit a fused Spur on the supply as the Alarm box is fused internally on the supply as it enters the box. At the time I thought this was O.K. as I understood the 3 meter rule to allow Down sizing and omiting of a fused spur at the point of connection to the ring main. As long as the run was less than 3 meters and the load to be suitably limited by protection at the end or along the supply cable. Since retiring I have had time to ponder these things. Any clarification would be a big help.
 
as he said^^^^^. normal practice is to fit a unswitched FCU (3A) adjacent to the alarm panel. but it's not unsafe. it's worked for 30 years ain't it?
 
At the time I thought this was O.K. as I understood the 3 meter rule to allow Down sizing and omiting of a fused spur at the point of connection to the ring main. As long as the run was less than 3 meters and the load to be suitably limited by protection at the end or along the supply cable.
I thought you could only apply that rule for connections within 3M of a cutout/meter or busbar chamber, not parts of a final circuit?
 

Reply to Applying the 3 meter rule. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
407
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
739
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
422
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
335

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock