Discuss Arcing on neutral at main switch in the Australia area at ElectriciansForums.net

Reaction score
8
Hello all, Been to look at a fault today which consisted of the lighting circuit tripping the mcb. When looking into it further no obvious fault became apparent. When I took a look at the d/b I found some scorch marks and melting of the plastic on the neutral rod from the load side of the main switch. The main switch is a 30ma RCD.Also when looking at one if the loops into a ceiling Rose I could see the start of some heat damage on the neutral there as well.I spent all day investigating all my dead test came back okay, ze values and RCD times okay. I do not think it is overload issue as it is a basement flat not many circuits, no major loads. The only other advice they gave was that they sometimes used the shower and the trip went and the could smell that nasty hot plastic smell.I have let it safe tonight but going back tomorrow hoping that the occupant in the flat above accommodating to let me investigate through her floor. Has anyone had a similar problem or any suggestions why the scor h marks. I have checked the terminations in the board and they Are okay , neutral nice and tight .Any input would be greatly appreciated
 
The common causes of heat at terminations is loose screws causing arcing or overtightened screws causing the wire to be damaged and the resistance of the damaged section causes heat. Corrosion and wiring that was previously annealed by overheating could also be a factor as well as general overloading or harmonics which is unlikely in domestic premises.. Either way I would remove the wiring, cut back and re-strip if possible and remake the terminations.
 
I am just guessing here but what type of lamps are they? If non incandecsants (flourescent lamps) it may be inductance. I may be wrong of course but.....
Is it wired in singles? Are the neutrals in the same conduit as the line conductors? It may be just a breakdown in insulation as you mentioned it was the breaker that wasn`t holding. It may be someone more experienced than myself on here can help.......
 
I agree with Marvo, sounds like a poor connection best to reterminate.
Another thing to check is the continuity through the actual RCD/where the plastic is melting. I have replaced several D.P switches or MCB's due to a very high resistance through one of the poles.
 

Reply to Arcing on neutral at main switch in the Australia area at ElectriciansForums.net

Similar Threads

Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
693
These are going to become the norm aren't they? I've been reading this...
Replies
10
Views
1K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Not the usual per-1966 sort of "no CPC in wiring issue" but plastic light switches in plastic back-boxes in trunking wired in singles. The lights...
Replies
3
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock