Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the Regulation supporting this Code 1/2?
I can see 411.3.1.1 but this relates to Lighting. If anyone could assist Id appreciate it, I know its a fault but...
Not the usual per-1966 sort of "no CPC in wiring issue" but plastic light switches in plastic back-boxes in trunking wired in singles. The lights have CPCs and measured Zs, RCBO trip-time, etc, all good. However, the actual switches lack a CPC.
Now I could run in a CPC to meet the last...
I am doing a new consumer unit install on a second story ex council flat. I’ve notice the mains come in in metal conduit with no CPC. On checking further I’ve seen they have split the neutral before the meter and joined an earth cable onto it creating a pme at the fuse board. I believe this can...
I all 4 bedrooms in a rented property, there are cheap metal electric wall heaters. By design their cables are made of two wires - no cpc.They are plugged into a socket circuit with 32 A MCB.How would you code that? AThe heaters are not part of the installation, do i need to put that in the report?
I have a couple of lights on a circuit that does not have a CPC. The light fittings are plastic but they have a metal trim that screws into the plastic body.
I wonder if anyone can advise me if these are deemed as safe considering the main body of the light fitting is plastic and the metal trim...
I've just installed a couple of additional 12v down lights and changed extractor fan in a bathroom. The lighting circuit is one with no CPC.
How would you complete a MEW?
Obviously tests are limited in this case, but where would you use LIM, X, - etc in the relevant boxes?
thanks.
Hi all,
Had a call from a customer saying her oven had broken. When the oven engineer went out he fixed the oven but told her she had "no earth on her kitchen sockets".?!?! He told her the other circuits ie the lounge and cooker, were ok but no earth to the kitchen ring final?! How can this be...
Probably going over old ground here but I have assessment soon on this job, new consumer unit fitted completed R1+R2 test at light pendants all ok but two way light was found to have no cpc at light switches although does have earth at pendant what can i do for my assessment have read esc...
Andysparky
Thread
aus
circuit
cpc
light
metal
nocpc
screws
switch
switches
I was asked to change a light fitting for a friend and replacing the old plastic pendant from a metal class I fitting but there is No cpc.
Without ripping out laminate flooring ect there is no no way i can get a cpc from the downstairs circuit, which this light is on.
The Upstairs circuit has...
All,
Looking for opinions please:
Just been to see a client who has had another sparky in who has connected up an outbuilding which has a number of 2 gang sockets and lights - all from a 13A spur off the ring - no RCD protection anywhere. He was due to change the CU but has said he won't...
Octopus
Thread
aus
change
circuit
class
client
cpc
fittings
lighting
lighting circuit
nocpc
was asked by a friend to put up some light fittings for his mum, changing from pendant to some fancy metal fittings, discover that there is no cpc on the circuit.
Running a cpc or redoing the whole circuit again from the CU is going to be difficult, newly decorated pace all laminate flooring in...
steve447
Thread
aus
circuit
cpc
earth
fittings
light
lighting
lighting circuit
metal
nocpc
hi - just changed some light fittings for a customer, tested and found no continuity from phase to earth. checked the CU - (earth present) and found a box above it containing 2 core and earth choc blocked to 2 core no earth. presumably when the last CU change (looks like eighties) they simply...
Folks,
Doing a bathroom job presently and none of the lighting circuits have a CPC....it's an old topic I know and I'm aware of of requirements so I'll not be fitting that fancy bathroom spotlight!
However, what in theory is wrong with *temporarily* borrowing a CPC from the adjacent...
Evening All....
Just been to look at job, CU upgrade and submain... which is still in rubber :eek:
But lights have got no cpc, metal fittings everywhere, old style round light switches:confused:
Customer wants to keep cost down, as usual... so wasn't sure where I stand. Idealy rewire all the...
Installed a double insulated in-line fan on friday, came to tests & no cpc continuity. Checked & tested back at spur & nothing there, Checked at nearest light fitting & still no joy. Its obvious there has been a lot of work at the property with a number of downlights on the lighting circuit...
Hi all
I have a customer with no cpc on the lighting circuit - property is a top floor flat with a flat roof above so no access above ceilings. I was looking at the possibility of installing class 2 lights - I've found lots of websites offering class 2 fittings but it's unclear exactly what...
andyww
Thread
aus
circuit
class
class 2
cpc
light
lighting
lights
nocpc
Hi guys, just after some advice, what do you do when you come up to a property with no cpc in the lighting circuit?
Do you run a sep cpc back to board? or can you run it from say the ring?
Just after some advice!?
Thanks for your time.
hi all,
got a cu to change on mnoday where both lighting circuits have no cpc.
done a few before and nearly always because home owner wants to keep price to a minimum :rolleyes:
i obviously mark it on eic and correctly label the cu so it all complies.
just wondered what others thought...
Hi,
I've been helping out a plumber mate of mine with the moving and changing of a few fittings in bathroom. One of which is a metal mirror light. However the bathroom lighting circuit doesn't have a earth.
They don't want the added cost of running back to the board, so was wondering...
YTSOxford
Thread
aus
circuit
cpc
customer
earth
lighting
lighting circuit
metal
nocpc