    EICR Code - Socket Radial - No CPC

    Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the Regulation supporting this Code 1/2? I can see 411.3.1.1 but this relates to Lighting. If anyone could assist Id appreciate it, I know its a fault but...
  2. P

    No CPC at light switches in plastic trunking

    Not the usual per-1966 sort of "no CPC in wiring issue" but plastic light switches in plastic back-boxes in trunking wired in singles. The lights have CPCs and measured Zs, RCBO trip-time, etc, all good. However, the actual switches lack a CPC. Now I could run in a CPC to meet the last...
  3. P

    Who do is responsible for the incoming suppy

    I am doing a new consumer unit install on a second story ex council flat. I’ve notice the mains come in in metal conduit with no CPC. On checking further I’ve seen they have split the neutral before the meter and joined an earth cable onto it creating a pme at the fuse board. I believe this can...
  4. Z

    Metal electric wall heaters - no cpc present.

    I all 4 bedrooms in a rented property, there are cheap metal electric wall heaters. By design their cables are made of two wires - no cpc.They are plugged into a socket circuit with 32 A MCB.How would you code that? AThe heaters are not part of the installation, do i need to put that in the report?
  5. M

    Plastic Light fitting with metal trim & no CPC

    I have a couple of lights on a circuit that does not have a CPC. The light fittings are plastic but they have a metal trim that screws into the plastic body. I wonder if anyone can advise me if these are deemed as safe considering the main body of the light fitting is plastic and the metal trim...
  6. W

    Minor Works Cert - No CPC

    I've just installed a couple of additional 12v down lights and changed extractor fan in a bathroom. The lighting circuit is one with no CPC. How would you complete a MEW? Obviously tests are limited in this case, but where would you use LIM, X, - etc in the relevant boxes? thanks.
  7. F

    No cpc continuity on ring final

    Hi all, Had a call from a customer saying her oven had broken. When the oven engineer went out he fixed the oven but told her she had "no earth on her kitchen sockets".?!?! He told her the other circuits ie the lounge and cooker, were ok but no earth to the kitchen ring final?! How can this be...
  8. A

    No cpc at light switches

    Probably going over old ground here but I have assessment soon on this job, new consumer unit fitted completed R1+R2 test at light pendants all ok but two way light was found to have no cpc at light switches although does have earth at pendant what can i do for my assessment have read esc...
  9. S

    No CPC on hall way lighting

    I was asked to change a light fitting for a friend and replacing the old plastic pendant from a metal class I fitting but there is No cpc. Without ripping out laminate flooring ect there is no no way i can get a cpc from the downstairs circuit, which this light is on. The Upstairs circuit has...
  10. O

    Lighting Circuit no CPC

    All, Looking for opinions please: Just been to see a client who has had another sparky in who has connected up an outbuilding which has a number of 2 gang sockets and lights - all from a 13A spur off the ring - no RCD protection anywhere. He was due to change the CU but has said he won't...
  11. N

    PIR records where there is no cpc

    What measurements do you record on the Schedule of Test Results for a circuit that has no cpc?
  12. S

    Lighting circuit no cpc

    was asked by a friend to put up some light fittings for his mum, changing from pendant to some fancy metal fittings, discover that there is no cpc on the circuit. Running a cpc or redoing the whole circuit again from the CU is going to be difficult, newly decorated pace all laminate flooring in...
  13. T

    no cpc

    hi - just changed some light fittings for a customer, tested and found no continuity from phase to earth. checked the CU - (earth present) and found a box above it containing 2 core and earth choc blocked to 2 core no earth. presumably when the last CU change (looks like eighties) they simply...
  14. steamboatwilly

    Bathroom Class I light but no CPC - Borrowing the CPC in Theory

    Folks, Doing a bathroom job presently and none of the lighting circuits have a CPC....it's an old topic I know and I'm aware of of requirements so I'll not be fitting that fancy bathroom spotlight! However, what in theory is wrong with *temporarily* borrowing a CPC from the adjacent...
  15. sythai

    Advice please.... no cpc on lights

    Evening All.... Just been to look at job, CU upgrade and submain... which is still in rubber :eek: But lights have got no cpc, metal fittings everywhere, old style round light switches:confused: Customer wants to keep cost down, as usual... so wasn't sure where I stand. Idealy rewire all the...
  16. J

    No CPC continuity

    Installed a double insulated in-line fan on friday, came to tests & no cpc continuity. Checked & tested back at spur & nothing there, Checked at nearest light fitting & still no joy. Its obvious there has been a lot of work at the property with a number of downlights on the lighting circuit...
  17. A

    No cpc on light circuit - class 2 lights?

    Hi all I have a customer with no cpc on the lighting circuit - property is a top floor flat with a flat roof above so no access above ceilings. I was looking at the possibility of installing class 2 lights - I've found lots of websites offering class 2 fittings but it's unclear exactly what...
  18. W

    No cpc at lights!

    Hi guys, just after some advice, what do you do when you come up to a property with no cpc in the lighting circuit? Do you run a sep cpc back to board? or can you run it from say the ring? Just after some advice!? Thanks for your time.
  19. flukey

    changing cu with no cpc in lighting circuits

    hi all, got a cu to change on mnoday where both lighting circuits have no cpc. done a few before and nearly always because home owner wants to keep price to a minimum :rolleyes: i obviously mark it on eic and correctly label the cu so it all complies. just wondered what others thought...
  20. Y

    No CPC on lighting circuit

    Hi, I've been helping out a plumber mate of mine with the moving and changing of a few fittings in bathroom. One of which is a metal mirror light. However the bathroom lighting circuit doesn't have a earth. They don't want the added cost of running back to the board, so was wondering...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock