teknojon
hi - just changed some light fittings for a customer, tested and found no continuity from phase to earth. checked the CU - (earth present) and found a box above it containing 2 core and earth choc blocked to 2 core no earth. presumably when the last CU change (looks like eighties) they simply connected to the old non-earthed cabling.
so - can i leave this as is and change the metallic fittings to plastic - or should i insist on earthing the whole lighting (circuits) - not checked the extent of the lack of earthing between lighting yet.
also - much more worrying, the 1x ringmain for the house (except the new kitchen ring installed during the dodgy 80's extension ) is again connected by 2 x 2c+e to 2 core. there is a cpc apparently connected to the garage consumer unit and hence back to the CU via the armoured cable's earth.
the ring is therefore earthed, back to the MET (unless the armoured cable fails) - so, should i recommend connecting each end of the ring direct back to the CU with new 2.5 mm 2 c+e (assuming there is earthing between the sockets themselves (have taken a couple of facias off and found cpc there)?
the current cu has 1 RCCB / isolator.
i don't want to have to disrupt too much decoration.
doing a proper check next week
any ideas would be great
ta
jon
so - can i leave this as is and change the metallic fittings to plastic - or should i insist on earthing the whole lighting (circuits) - not checked the extent of the lack of earthing between lighting yet.
also - much more worrying, the 1x ringmain for the house (except the new kitchen ring installed during the dodgy 80's extension ) is again connected by 2 x 2c+e to 2 core. there is a cpc apparently connected to the garage consumer unit and hence back to the CU via the armoured cable's earth.
the ring is therefore earthed, back to the MET (unless the armoured cable fails) - so, should i recommend connecting each end of the ring direct back to the CU with new 2.5 mm 2 c+e (assuming there is earthing between the sockets themselves (have taken a couple of facias off and found cpc there)?
the current cu has 1 RCCB / isolator.
i don't want to have to disrupt too much decoration.
doing a proper check next week
any ideas would be great
ta