Search the forum,

Discuss no cpc in the Australia area at ElectriciansForums.net

T

teknojon

hi - just changed some light fittings for a customer, tested and found no continuity from phase to earth. checked the CU - (earth present) and found a box above it containing 2 core and earth choc blocked to 2 core no earth. presumably when the last CU change (looks like eighties) they simply connected to the old non-earthed cabling.
so - can i leave this as is and change the metallic fittings to plastic - or should i insist on earthing the whole lighting (circuits) - not checked the extent of the lack of earthing between lighting yet.
also - much more worrying, the 1x ringmain for the house (except the new kitchen ring installed during the dodgy 80's extension ) is again connected by 2 x 2c+e to 2 core. there is a cpc apparently connected to the garage consumer unit and hence back to the CU via the armoured cable's earth.
the ring is therefore earthed, back to the MET (unless the armoured cable fails) - so, should i recommend connecting each end of the ring direct back to the CU with new 2.5 mm 2 c+e (assuming there is earthing between the sockets themselves (have taken a couple of facias off and found cpc there)?
the current cu has 1 RCCB / isolator.
i don't want to have to disrupt too much decoration.

doing a proper check next week

any ideas would be great

ta

jon
 
hi - just changed some light fittings for a customer, tested and found no continuity from phase to earth. checked the CU - (earth present) and found a box above it containing 2 core and earth choc blocked to 2 core no earth. presumably when the last CU change (looks like eighties) they simply connected to the old non-earthed cabling.
so - can i leave this as is and change the metallic fittings to plastic - or should i insist on earthing the whole lighting (circuits) - not checked the extent of the lack of earthing between lighting yet.

Assuming that you have no presence of CPC conductors at the fittings, then you can follow the methods as illustrated in the best practice guide on this topic.


also - much more worrying, the 1x ringmain for the house (except the new kitchen ring installed during the dodgy 80's extension ) is again connected by 2 x 2c+e to 2 core. there is a cpc apparently connected to the garage consumer unit and hence back to the CU via the armoured cable's earth.
the ring is therefore earthed, back to the MET (unless the armoured cable fails) - so, should i recommend connecting each end of the ring direct back to the CU with new 2.5 mm 2 c+e (assuming there is earthing between the sockets themselves (have taken a couple of facias off and found cpc there)?
the current cu has 1 RCCB / isolator.
i don't want to have to disrupt too much decoration.

doing a proper check next week

any ideas would be great

ta

jon

(R1&R2) tests should solve this problem. Either you have them or you don't, if not then necessary measures will need to be taken.
 
cheers for the reply

i simply don't know the extent of the earthing from the original wiring. the older part of the house has no earthing to the cu. the loft conversion builders of the 80's must have earthed the old house ring back to the garage cu, but phase and neutral to the house cu. dodgy bit of wiring that does leave the sockets with earth at least. i very much doubt that there will be any cpc's between the sockets, except perhaps if someone's added to or spurred. the customer has been warned that i may need to at least partially re-wire.
how safe is the current instal tho? it's earthed.

as for the lights - when working in the loft space i found newer cable with cpc. so at some point there is none - also took one switch cover off - no cpc. there could be alot of work and damage here to remedy. would class 2 fittings resolve this satisfactorily?

not that i don't want to do all the work - rewire 2 lighting circs and a ring, just wanted to give the fella options, they aren't wealthy and i'd like to safely make the house compliant at lowest cost ideally.

i'm back there later this week for a full check and, as i said, would like to offer options

ta
 
Class II fittings will solve your problem on the lighting yes, but really if you have found all these other problems you have a care of duty to advise the customer that there is a good chance that the installation is not safe.

I know in todays market money is tight, but you are honest and I'm sure you are not going to take advantage. If it were me I would suggest a ful PIR to be done, as you have done quite a bit of the survey by the sounds of things you could quote a competative price. Advise them that whatever remedial work is needed, you will quote for it, and will deduct a percentage of the PIR cost from the quote if the work was given to you.

I think this way is fair, it will show them your fair, and you will not be out of pocket.
 
thanks malcolm
- you sound an honest fella like me

Cheers Jon, though never helped me to much when I had to wind down my compnay :D, but thats another story. but I find that being honest usually pays, helps you sleep at night, and I'm a great believer that what goes round comes round.

All the best mate glad there are sill good guys out there in our industry.
 

Reply to no cpc in the Australia area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
961
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
801
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock