A couple of questions if I may...

What type of cable is it going to be run in?
How loaded are the other 3 cables?
cable will be 10mm T&E.the other cable runs are 2.5mm T&E one of which has 2 double sockets on it ,one of which has microwave plugged in and the other has the washing machine and tumble dryer .and the other cable has a single socket doing nothing and a double rcd socket which will have a dishwasher plugged in.
 
If going with a separate CU then any of the "shower" units should do fine - 63A RCD and 40 or 45A MCB.

You'll want one with a good amount of space in it to nicely terminate 10mm, but the current metal ones do tend to have more space in now than they used to.

It might pay to get a 2 or 3 way one with blanks to give you the extra space (and the possibility of adding maybe a 6A or 16A in the future.
thats good news ,ive checked and there is room in the henley block for another set of tails so i can fit a 63Arcd with a 40Amcb shower unit ,wont need expansion in future ,just as long as the 40A mcb will be enough otherwise ive got to find a 45 and it most likely wont be same make ,and i dont want to go up to a 50 for the sake of matching it all
 
cable will be 10mm T&E.the other cable runs are 2.5mm T&E one of which has 2 double sockets on it ,one of which has microwave plugged in and the other has the washing machine and tumble dryer .and the other cable has a single socket doing nothing and a double rcd socket which will have a dishwasher plugged in.
Thanks.
I did a Procerts calculation using the info you gave, which points to 10mm minimum.
Screenshot_20210423-174524_Electrical Tools and Reference.jpg
 
The pedant in me needs to point out that Uo is 230, not 240....... (although you're better off using 240-243 for real-life purposes!)
 
Indeed. I was also going to point this out. Using 230 volts results in 41.3 amps, so a 45 or 50 amp OCPD would be needed.
Which in itself raises an interesting question...... should we actually ignore the 'official' nominal voltage when doing cable calcs and instead use what we all know is realistic in order to err on the side of caution??
 
thankyou all for the advice ,i will be running 10mm T&E from a seperate CU which will have a 2 pole 63A 30mA RCD device and a 50A MCB Type B fed from a seprerate set of 16mm tails from the henley block
 

Reply to ariston water heater install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
We own a small, one bedroom flat (built 1989). An EICR inspection raised three C2 observations and recommendations: (A) The shower cable, and...
Replies
8
Views
4K
Hi folks. I'm asking so that I can do some planning, and then hire a local electrician to do the work. WHAT: This is my first question, ever...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock