- Reaction score
- 2,853
Yes, you got itThank you, I’ve only got the brown book but looked up the tables. Basically the cable is de-rated to 46A so it operates at 70 instead of 90 degrees?
Discuss Assistance with my installation in the UK Electrical Forum area at ElectriciansForums.net
Yes, you got itThank you, I’ve only got the brown book but looked up the tables. Basically the cable is de-rated to 46A so it operates at 70 instead of 90 degrees?
We do have to remember though that bs7671 forbids the use of pme earthing for some types of installations.I don't believe this to be true @Dartlec, I believe this is a (rather persistent) myth .
I have it in writing from 3 DNOs (every one that I have contacted so far) that they have no special requirements regarding earthing arrangements at outbuildings.
Your point is...?We do have to remember though that bs7671 forbids the use of pme earthing for some types of installations.
You said, "I have it in writing from 3 DNOs (every one that I have contacted so far) that they have no special requirements regarding earthing arrangements at outbuildings."Your point is...?
how many faults per year on pme lost neutral very little the power lines are monitored ,you have got more chances of being kissed on the lips of a giraffe .I have it in writing from 3 DNOs (every one that I have contacted so far) that they have no special requirements regarding earthing arrangements at outbuildings
One death would be one too many.how many faults per year on pme lost neutral very little the power lines are monitored ,you have got more chances of being kissed on the lips of a giraffe .
its like throw a frying pan in the air in a crowd which unlucky one get it first .One death would be one too many
We do have to remember though that bs7671 forbids the use of pme earthing for some types of installations.
That would depend on what the shed is made of.Yes it is prohibited for certain installations, but not garden sheds.
Reply to Assistance with my installation in the UK Electrical Forum area at ElectriciansForums.net