Backup fuse for SPD?

Discuss Backup fuse for SPD? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi everyone
smiley-smile.gif
,

should there be a backup fuse for Q0.1-SPD and what size? Schematic is attached.
Fuse backup.jpg
 
Check the SPD manufacturer's data sheet.

There is always some sort of over-current protection specified but it can be as high as 315A fuses in some cases, or as low as 32A MCB in others. It can also depend on just how the connections to the SPD are made, say if "V-wired" with the load current flowing through the SPD's terminals, or if the SPD is spurred of a terminal block.

It might be met by the supply fuses so nothing else is needed, otherwise some fuses or MCB would be needed.

Remember that SPD need short low inductance connections to be effective, as well as a minimum cable size for the surge I2t heating effects. So a fuse is probably better than a MCB on that front, and if selecting a MCB go for the C or D curve ones to reduce the inductive aspect of the "instant" magnetic trip. UK regs have max 1m total cable length, ideally less than 0.5m, so SPD within 0.25m of the supply and main earth terminals including any OCPD route.
 
Last edited:

Reply to Backup fuse for SPD? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock