Discuss Surge Protective Devices in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Hi guys, could someone help with the following please? The scenario is:

Domestic property supplied via three phase (with a 3P main DB, NO SPD).
Tails split via henley blocks, and a second single phase DB installed; this DB has an SPD for it and it's circuits.

Now, normally with a single phase property, if the first DB had no SPD but the second DB was fitted within 10M of it, the installation as a whole could be regarded as protected, and that would be that. However, in this case, as the SP DB is more than 10M away from the main 3P board, only the circuits in my board are protected. However, is there a requirement that I should also install a three phase (Type 1) SPD in the main 3P board, in order to protect the circuits supplied by that board too, or is my responsibility only actually limited to the DB I installed? Many thanks in advance for any advice!
 
If you have only installed the board with the SPD your remit stops there. Imagine a site with hundreds of boards, where do you draw the line.
 
If you have only installed the board with the SPD your remit stops there. Imagine a site with hundreds of boards, where do you draw the line.
Thank you for the advice; I did figure it would be in the realms of discovering, say, a 10mm earth cable in a property, and having no more responsibility for that, other than to recommend that it's upgraded to 16mm. I just wanted to check if this situation was any different, so cheers for the response.
 

Reply to Surge Protective Devices in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
821
Hi, I’m at a job on a grade 2 listed property with 5 different single phase distribution boards, the client wants sockets moved to new locations...
Replies
11
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
478
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
523
Wallbox Fuse Box Lite Single Phase has anyone used one of these? I've installed one feeding a Pulsar Max, the Pulsar Max is set to 32Amp max. The...
Replies
0
Views
215

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock