Discuss Basic Megger Use in the Commercial Electrical Advice area at ElectriciansForums.net

S

Stanley36

Good day all.

I was wondering how you actually go about using a megger to test the quality of insulation of a motor, I understand why you would do the test. If you were to test it at the motor starter and you have isolated the circuit would you need to disconnect the wires going to the motor from the contactor or overload first?

Also would you need to disconnect the motor links (on a 6 terminal DOL motor) to carry out phase to phase resistance tests.

Any other Noddy information about this would be much appreciated :).

Many thanks
 
if it's the motor you're testing, then isolate, diss feed at motor, remove links, then test phase-phase and each phase to E.
 
You would be wise to know the type and layout of the particular motor,to eliminate false readings due to suppressors,capacitors,thermal and centrifugal switches,etc.

You may get a result which shows an issue,but whether that is a failed winding,or just an chaffed link wire,could be the difference between an expensive strip-out...or a simple hours' repair.

Fully understanding the internal connections and function,can allow you to individualize your tests,for example,knowing where and how a centrifugal switch is wired,will enable three tests to be applied to that item,all be it with a little help, on one :blush5:
 

Reply to Basic Megger Use in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
441
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
652
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
796
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
595

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock