- Reaction score
- 8,777
No, I wouldn't remove the panel (oh that all home owners would think in such an obliging way!)Hi again Tim, when I get it tested, how does the tester assess the supplementary bonding? If it is by inspection should I remove the bath panel so that they can see the pipes?
A lot of installations would meet the 3 requirements in section 701 (automatic disconnection of supply for all circuits in room, RCD protection for all circuits in room, and all extraneous conductive parts are bonded) which would mean supplementary bonding isn't required.
You don't have RCD protection for all circuits in room, so be default supplementary bonding is required.
So next question is are there any metallic parts that could introduce a potential in the bathroom (extraneous conductive parts).
If there are then the CPC of all circuits in the room need to be connected to the extraneous conductive parts with supplementary bonding.
From what you've said it sounds as though the copper pipe to the toilet cistern might be a contender.
You haven't mentioned any heating in there - is the a radiator / towel rail with metal pipes?
Having determined that supp. bonding is required, and there are items that require it, it's usually quickest to use continuity tests to check the resistance between the items is low enough to keep the touch voltage below 50v. There's a formula in the regs for how low it needs to be.