Hello all,

I am thinking of adding battery storage to my existing setup to increase self-consumption and provide backup for power cuts. Currently I have 16 x 230W panels feeding 2 + 2 kW StecaGrid inverters installed in 2011.

If I were to add for example a Victron MultiPlus 48/3000/35-50 in their Hub 2 configuration (i.e. the inverter/charger is connected to the incoming grid and the StecaGrids connected to the AC out) what are the regulatory requirements and the implications for my existing MCS certification?

Specifically, do I need to provide external anti-islanding protection or is the transfer switch in the MultiPlus sufficient (the internal earthing relay alteady meets G59)? If the new setup still cannot export more than 16A is the work notifiable to the DNO? Does it need to be done by an MCS contractor? Will it affect my current FIT contract?

All contributions gratefully received!
 
I'm not sure of the exact set-up you are proposing but you would need to ensure that you were not charging the batteries from the grid and then putting the output through your FiT generation meter via your existing inverters.

You should check the terms and conditions in your FiT contract with your electricity supplier to ensure you follow any required notification procedure of changes to your system.

Nothing really to do with the DNO although it would be polite to send them an updated system schematic.
 
Thanks for that Ted.

Am trying to find a good solution to

  1. Maximise self consumption
  2. Provide backup for power cuts
  3. ideally with island operation so that solar power extends operating time when grid is down.

No, the proposed arrangement would not be able to put energy from the batteries through the solar TGM. It's the Hub 2 configuration on p5 of the following paper (sorry, I haven't found a way to paste their diagram here) http://www.victronenergy.com/upload...ce-with-the-Victron-Energy-Storage-Hub-EN.pdf i.e. the solar inverters (and meter) would be connected on the load side of the battery inverter/charger. So it would be for this latter inverter to determine when grid voltage is present and if not to automatically disconnect it, currently this functionality is provided by the solar inverters as a condition of their G83 approval hence the possible interest of the DNO (lest its personnel be electrocuted by my equipment!)

Confusingly Victron also make a Solarswitch for changing the solar inverters over from grid side to load side of the battery inverter. The brochure http://www.victronenergy.com/upload/documents/Brochure-Solarswitch-SAL064122020-02-1103-EN_web.pdf also says

"In some countries grid impedance measurement is required as an additional safeguard against islanding. The output impedance of the MultiPlus will not match the impedance of the grid. Therefore the grid impedance monitoring function of the grid inverter must be switched off for proper functioning of the system. In countries where grid impedance monitoring is required, an additional grid monitoring module must therefore be inserted betweenthe SolarSwitch and the PV feed-in meter."
which would I think also attract the interest of the DNO, is impedance monitoring a required feature in the UK?

Will follow up with Victron and my FIT contract and post anything of interest back here.
 

Reply to Battery Storage And Uk Regulatory Compliance in the Green Energy Forums | Green Energy Hub area at ElectriciansForums.net

Similar Threads

I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board...
Replies
4
Views
1K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
548
I am in the process of designing a system for deployment in Southern Africa and looking for some help/input from fellow solar installers and...
Replies
3
Views
2K
sgt_woulds
S
Hi All Planning an off-grid solar system and I’m pretty confident about most of it except for one thing - earthing. I believe the inverter I...
Replies
1
Views
7K
J
I am developing a prototype garden workshop design that has an off-grid power supply. The current setup is 300Wp PV, MPPT charge controller with...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock