Hi there I’m boarding my attic and the wires are going over the joists,

I know I can chisel a grove in the chipboard board or take the wires out of light fixture.

I was just wondering would it be a bad idea just to made a grove in the top of the joist with a round rasp just big enough for the wire to sit in the joist below the board?

I know you can also drill hole in middle of joist just wondering is it a bad thing to make notch in top of joist?
 
I would say it would depend upon how deep the joists are. They should ideally only be drilled or notched in certain locations. If you google, where to drill joists, you should find plenty of guides. You should consider using safe plates as well, if you go down the notching route.
 
Hi - I don’t run twin and earth cables in joist notches due to the risk of damage from a future nail or screw. Here’s an extract of the Electrician’s Guide to Building Regulations on the topic.
C9171F11-841D-4C29-936A-05F4DB776B57.jpeg
 
Hi - I don’t run twin and earth cables in joist notches due to the risk of damage from a future nail or screw. Here’s an extract of the Electrician’s Guide to Building Regulations on the topic.
View attachment 57818
Are the rules you quote the same for rafters, joists are not the same as roofing trusses are they? just wondering, after all they are not as robust as floor joists. smaller in all planes especially in new houses.
 
Last edited:
Are te rules you quote the same for rafters, joists are not the same as roofing trusses are they? just wondering, after all they are not as robust as floor joists. smaller in all planes especially in new houses.
good point. i'd be wary of drilling modern roof trusses. the ideal way would be to notch and fit plates. that also means that the cables don't need disconnecting.
 
Are the rules you quote the same for rafters, joists are not the same as roofing trusses are they? just wondering, after all they are not as robust as floor joists. smaller in all planes especially in new houses.
Hi Pete - I hope you are well :) .
The minimum depth for unprotected cable should still be 50mm below the surface, but you’re right the strength of the beam needs consideration, which would likely be on a scale of ok to oh dear :) .
 

Reply to Boarding attic, wires over joists, advice needed. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
683
I have a fuseboard change I need to do soon I’m putting in a FUSEBOX 7 or 10 way RCBO+ SPD My only concern is how I should run the pyro cables in...
Replies
16
Views
1K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock