Discuss Body’s resistance with mcb only in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Wilson12

-
Trainee
Reaction score
3
If there’s 230v and the body’s resistance is high ..
Meaning the current will be very low but enough to kill you.
Can we get electrocuted without having a 30ma rcd to stop this as the 6amp breaker will not have tripped ?
 
We did some very crude calculations on this sort of thing at college

Assuming dry skin , no wet floor etc etc

Iirc a b curve mcb would not trip if a person grabbed the live wire
 
I don’t understand why rcds are additional protection then because loads of places just have mcbs which don’t protect people
MCBs provide overload and fault protection. RCDs protect from silly fingers directly contacting parts which are live.
 
The effects of electric shock are very variable and subject to a whole range of different considerations.

The resistance (or impedance) of the body is one consideration but then you have to say where the current travels, hand to foot, foot to foot, hand to hand, head to hand and so on. The resistance varies widely.

How good a contact is there to the source of supply?
How wide a contact is there to the source of supply?
How wet is the body and with pure water or salt water?

On a very basic level the hand to hand resistance of the human body in dry conditions with a wide contact area is generally taken to be about 1000Ω.
This could be the equivalent of holding onto an earthed railing and putting the other hand around a live cable.
Using I =V/R this would give you a current through the body of 230mA.
No circuit breaker (0.5A minimum for 60947-2) will ever disconnect at this level.
Therefore you are then looking at the period of experiencing the shock, based solely on how long contact is maintained, to decide on the effects of the shock.
Above 200ms there would start to be the chance of irreversible effects including death from heart fibrillation.

If the body is wet with water containing salts dissolved in it (say sea water) then the resistance may be halved.
Similarly the resistance from hand to foot may be three quarters.

If you experienced a 500mA shock in this way you would be immediately into the chance of electrocution by heart fibrillation.

The use of circuit breakers is only there to prevent cables overheating and burning, it is not designed to protect people from electric shock. Though it does have the effect off ensuring the faulty circuit is off when someone starts looking at it.

The only protection for people from electric shock is chance and rubber soled shoes!

That is why RCDs are so important for safety.
 
Thanks that clears it up I know rcd haven’t been around as long as overload but

It seems crazy then that there’s soo many places without rcd protection and it’s classed only as additional protection
Surely seeing a consumer unit without rcd protection should be as serious as seeing a undersized cable or c1
 
When I was a trainee there were no RCDs as we know them in practical use in installations however what may seem counter-intuitive is that fatality from electrocution wasn't very much different to today, the main cause of death from electrical installations and products is usually the fires they cause which is still the case.
 
RCDs are used where ever there is a danger of persons coming into contact with live parts.

first, was sockets for outdoor use..... cutting mower/hedgetrimmer cables leaves exposed live parts, probably on wet grass, operator picks up cut cable.... dead.

second, was more sockets, damaged appliance flex exposing live conductors.operator dead.

third.. cables buried in walls, homeowner drills for new shelves, hits cable..... dead.

and so-on and so-on.
 
first, was sockets for outdoor use..... cutting mower/hedgetrimmer cables leaves exposed live parts, probably on wet grass, operator picks up cut cable.... dead.

third.. cables buried in walls, homeowner drills for new shelves, hits cable..... dead.
The lack of easy to find statistics is quite predictable--
No DIY store will sponsor their collection ..
May put punters off buying power tools
.... (spice racks are dangerous)
 

Reply to Body’s resistance with mcb only in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
274
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi! DIYer here. I have an MCB running to a cooker isolator switch. The RCD connected to this set of MCBs is tripping and isolating the cooker MCB...
Replies
4
Views
753
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
770
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock