Hi! DIYer here. I have an MCB running to a cooker isolator switch. The RCD connected to this set of MCBs is tripping and isolating the cooker MCB is the only way to stop it. So, clearly a fault on this line.
I‘ve disconnected the cooker and the same fault exists. I’ve tested the cable for continuity and resistance. There’s a break / fault in the CPC line from distribution board to isolator switch. I’ve isolated the cable at several accessible points and discovered that the break is on a section that runs under a concrete floor.
Running a new cable is very tricky in my situation but may be the only answer. But….. as I have good resistance and continuity on the live and neutral lines, could I use the CPC from a ring close to the cooker isolator?
As stated, I’m a DIYer so be polite if this is a stupid idea.
Thanks in advance.
I‘ve disconnected the cooker and the same fault exists. I’ve tested the cable for continuity and resistance. There’s a break / fault in the CPC line from distribution board to isolator switch. I’ve isolated the cable at several accessible points and discovered that the break is on a section that runs under a concrete floor.