Discuss Boiler & 2 port valve problem in the Central Heating Systems area at ElectriciansForums.net

Reaction score
1
Hi,
I have just had a problem last night with my h/w & central heating system,
I have found out the boiler has been stopping and starting without the c/h 2 port valve opening,
I have tested the circuit and discovered it is the micro switch in the valve that must have stuck in the closed position when I turned the stat off last night.
My question is - instead of the grey wire being a permanent supply to the micro switch, can I move it to the terminal with the brown wire which only becomes live with the stat,
That way if the micro switch sticks it will still be controlled else where and won't send a call to the boiler all night?
 
No don’t do that, but you can move the little handle on the side of the two port valve that should lock into place to leave it permanently open.

Is it the hot water or central heating 2 port valve?

This is a temporary fix only.
 
now you’ve got me thinking. My previous post may not be too helpful.

I’m not sure why 2 port valves need a permanent live at all.

in a normally closed 2 port valve surely a switched live feed via a thermostat would be enough To make it open and sent a call to boiler and pump.

Hopefully someone else can pop along and tell us why.
 
I think the micro switches are used to preventing one valve making the other valve permanently open. Guess as the other valve micro switch is still working, you could do as you suggest, as a temporary fix.
 
Yes that will be fine to do, just means the load of the boiler will be going through the programmers relay rather than the micro switch but should be ok anyway, shouldn't get any back feeds or other valves opening
 
Last edited:
YES your 100% right Midwest, Thank you.
I can see now that the H/W calling would also send a feed to the C/H valve and open it as well,
I can switch off the H/W and use the element for now until i get a new valve,
Thanks again.
 
Yes that will be fine to do, just means the load of the boiler will be going through the programmers relay rather than the micro switch but should be ok anyway, shouldn't get any back feeds or other valves opening

No it isn't because it will get a backfeed from the other valve(s) if they are on when the s/l goes off. Thats the whole reason the grey wire was added to valves.


[automerge]1574528946[/automerge]
Its the C/H 2 port micro switch that stuck last night,
is there a reason the micro switch cant be a switched live

It can't be the switched live from the thermostat because it would suffer a backfeed from other valves. Some early 2 port valves suffered this problem because the microswitch was internally connected to the motor L, which was fine if here was only one valve but a relay was needed to use them in a S plan style system.

It can be connected to the switched live from the programmer of absolutely necessary as the thermostat would then interrupt any backfeed to prevent overheating, but you will still get some backfeed until the thermostat switches off.
 
Last edited:
Edit: realised that as it is CH valve it must be physically closed or you would have noticed by the rad temp.

As SJT & DS note, feeding the microswitch grey PL feed from the same controlled supply as the motor can cause backfeeding and incorrect operation if the orange output wire is commoned between multiple valves. One valve on its own will open and close and control the boiler correctly, but as soon as multple valves are open at once, a circuit is established via the microswitches that links their motors together. They will all remain open and the boiler fired while any of the controls is still calling for heat. When that goes off, all valves will close at once.
 
Pretty much covered,here,but it is worth noting,that the mechanical lever,to open the valve manually,does not always open it completely. Some are just for drain/bleed purposes.

On occasion,this restriction,can cause the boiler to trip on the over-heat stat.
 
I have cleaned the micro switch and it seems to be working ok now but i think i will run the permanent live that feeds the micro switch through a n/o contactor and control the coil from the room stat feed,
that way if the micro switch fails again the boiler will still switch off.
 

Reply to Boiler & 2 port valve problem in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
659
(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Replies
4
Views
1K
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
711
I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock