Besides finding a slug in my bathroom this morning- via the hole in the wall for the bonding.. should this earth bonding wire connecting my gas box be boxed in or is it ok outside as it is? Many thanks

IMG_6060.JPG
 
"where practical"
Yeah OK, but he could have taken the bond straight into the service box, same route as the internal gas pipe.
 
BG have a nasty habit of doing this. as pete said, bond shoule be to gas inside the property within 600mm of point of entry ( with murdoch's proviso of where practicable). there's no requirement to go to the external meter box (unless maybe when there's a branch in the pipework in tsaid box).
 
It may have been the best route externally, else it might of had to be clipped inside surface, I would not want that.
 
The gas bond should be inside your house, quite why the electrician has ran the cable outside is debatable, perhaps there is some difficulty in locating the pipe inside your house
It’s only the gas guys that state it should be in the meter box BS7671 says it should be as close to the entry to the building as practicable and before any tees/branches
 
are these the same gas guys that strap unnecessary bonding across all the boiler pipes?
 
Ones about gas pipes and gas, the others about electrics and electric cables
and unless I’m mistaken that is definitely a cable therefore p**s off gas regs, you know the only reason they want it there is so they can be sure the pipe is bonded when changing the gas meter because they are supposed to put croc clips across the supplier and consumer side in case either of the pipes are carrying any voltage and create an arc when the gas meter is disconnected wonder who set their hair on fire for that to happen:tearsofjoy:
 

Reply to Bonded external wiring to gas- should this be boxed in in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
924
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
764
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
931
L
WIRING FOR WALL SMART SWITCH FOR CEILING FAN/LIGHT Just bought a smart wall switch for a ceiling fan/light currently connected to a single switch...
Replies
0
Views
736
littletwinn
L
Howdy DIY soldiers, first post here. My question comes down to whether it would be particularly unsafe for me to temporarily wire nut and tape a...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock