I always run the balance between options.
Option 1 - supplementary bonding in accordance with 415.2.1
If there is a fault of poor cabling etc contacting the worktop and the person with wet hands, there is a big bang, no current goes through the person to speak of , no one dies, you don't go to court.
Option 2 - it's not mandatory to bond so no bond.
If there is a fault of poor cabling etc contacting the worktop and the person with wet hands, the current goes through the person, even though the rcbo trips (or perhaps fails to) the shock is still sufficient to cause serious injury or death, you go to court, but can prove you did comply with the minimum requirements, so would likely be able to fend off any charges etc.
That's my reasoning! I would prefer the former rather than the latter.
As for the Connections, take a look at 415.2.1, it makes it fairly clear what is suitable.
I would bond between pipes, tables and the earth/cpc points of the socket outlets all locally.