If you were to test a metal staircase on the side of the house on insulation resistance and it gave you a dead short. Would that need bonding. Test was done at the MET with all parallel paths disconnected. Staircase next to class 1 metal light fittings
 
Last edited:
It would need an ohm resistance test to determine if this needed MPBC to it.
If the Class1 can be touched simultaneously with the Staircase then it certainly would need it.😎
 
IMG_8204.jpeg
 
Great thanks for the advice. Am I right in thinking though, although not the best way to test...if the IR is below 0.0067Megaohms then it would certainly need bonding. My results were 0.000 Megaohms
 
Great thanks for the advice. Am I right in thinking though, although not the best way to test...if the IR is below 0.0067Megaohms then it would certainly need bonding. My results were 0.000 Megaohms
0.02 MΩ, then the part in question is considered as unable to introduce a shock risk and, as such, won’t require bonding.
 

Reply to Extraneous metal staircase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
626
100 volts on a metal ceiling grid when measuring from the Met to the ceiling grid Only when lighting circuit (led panels ) is on it goes away if...
Replies
7
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
752
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock