Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
62
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
 
If they are in good contact with earth(generally below the foundations) and meet the definition of an extraneous conductive part then They will require protective bonding to the MET
 
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
Have you tested the conduits to see if they are extraneous?
 
If the cable installed inside the conduit is insulated and sheathed such as twin&earth , then does it still need to be earthed as you effectively have double insulation unlike singles?
 
Insulated and sheathed is not the same as double insulation.
No it’s not but do you see were I’m coming from?
The added protection you have with twin & earth is it necessarily needed to earth the conduit?
Perhaps if buried in the floor against impact yes but otherwise I’m not convinced.
Open to discussion
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
 
Last edited:
As far as I can see, the reg that requires the earthing of exposed conductive parts is all encompassing and makes no exceptions.

The debate would be whether a part is an exposed conductive one or not.
 
That was my point but you made it in a much less smart arsey way. :)

I blame too much paperwork.

my apologies to Ian for said smart arse manner. :)
 
Well as per guidance note 8 and regulation 412.2.4.1 A cable complying with the appropriate standards having a non metallic sheath is deemed to provide satisfactory basic protection and fault protection as does an item of class 2 equipment.
Class 2 equivalence aas pvc insulated and sheathed cables.
Hence containment such as metal tray or basket need not be earthed.
Cables in conduit are fully enclosed but I feel meet the same requirement
 
411.3.1.1 is the reg that asks for earthing of exposed conductive parts. It makes no exception I can see nor references any of the regs pertaining to reinforced or double insulation.
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
T&E does not have reinforced insulation it has one layer of electrical insulation and an overall sheath which provides protection for the electrical insulation.
 
Well it’s deemed to provide satisfactory basic and fault protection as does an item of class 2 equipment.
I’m aware that every one bangs on about twin and earth is not class 2 blah blah but there it is.
Check out guidance note 8
 
On second thoughts, I don't think T&E does satisfy the requirement to deemed double insulated.
I believe the CPC has to also be insulated and sheathed to comply.
I've heard that before in respect of bringing cable into class 2 accessories. Flex is acceptable because the cpc is insulated to the same voltage as the live conductors.
 
The cpc only needs to carry fault current so it’s irrelevant if it’s not sleeved in this case as it’s not classed as a live conductor
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
Insulated and sheathed cables do not provide either double or reinforced insulation. They merely provide mechanical protection.
 
Insulated and sheathed cables do not provide either double or reinforced insulation. They merely provide mechanical protection.
Wiring systems are deemed to be double insulated if adequate mechanical protection of the basic insulation is provided by a non-metallic sheath or non-metallic conduit.
 
Insulated and sheathed cables do not provide either double or reinforced insulation. They merely provide mechanical protection.[/QUOTE I would say that any non metallic sheathed cable whether single core, multi or flat t&e affords protection against basic and fault protection contact much like class 2 equipment but isn't to be regarded as class II in itself.
 
To be double insulated you require two layers of "electrical" insulation or a single layer or more of reinforced insulation.
 
Conduit is part of the electrical installation, it doesn't compare with a double insulated (class2) metal light fitting. So would the disbelievers run a 3 core (L,N&E) swa under the floor without earthing the armour?
 
Conduit is part of the electrical installation, it doesn't compare with a double insulated (class2) metal light fitting. So would the disbelievers run a 3 core (L,N&E) swa under the floor without earthing the armour?
The armour needs glanding so by definition is always an exposed conductive part so it’s not the same is it
 
The armour is part of the overall construction of the cable
Conduit is not
Insulated and sheathed cables gives satisfactory protection against basic and fault protection is all I’m saying
 

Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
270
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
916
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock