Discuss Bonding the array in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

J

jcarlie

Evening guys

I know this one has been done to death, just wanted to share my proposal for an installation we are about to install.

Fronius TL 3.6 inverter
PME supply
Velux window, although im pretty sure that the array will not be accessible from this window.

After reading the DTI i have come to the conclusion that if i carry out a R2 test between the array and the MET and record a result of greater than 22K ohms then the array will be classed as isolated from the installation and therefore not an extraneous conductive part, thus avoiding the need to bond the array.

What is the general stance of others regarding this?

Cheers
 
err, surely it's not an IR test either. Your testing the continuity (resistance if you like) of the array to earth.
banging 500v through the array won't prove anything, except that it has no insualtion resistance
 
Moggy to test that a piece of metal work is an extraneous conductive part is an IR test, which is where we get the 22Kohm value from.

You IR test between the main MET and the piece of metal work and anything over 22KOhm is not an extraneous conductive part
 
bonding the array because of a velux window is because of direct contact, however you say even though there is a velux window the array is still not accessible to direct contact so not required is it. imo (tin hat on)
 
I would take the view that if the array is within touching distance of the velux window then it would be in the equipotential zone, if you cannot access the array from the window it is outside the equipotential zone
 
I can stand by my back door and touch a old pair of secateurs that my lass left there while pruning the roses and are a nice piece of metal.........................where do they stand regards the equipotential zone?

If your back door is the kitchen, it is full of equipment in there, I know because I have seen it while walking through, her indoors spends hours in there..
So if that is the case bonding will be required, or you could move the secatuers further out in the garden..
 
If your back door is the kitchen, it is full of equipment in there, I know because I have seen it while walking through, her indoors spends hours in there..
So if that is the case bonding will be required, or you could move the secatuers further out in the garden..
but only while hovering, otherwise you might risk becoming an extraneous conductive part yourself and some passing spark / plumber / kitchen fitter might bond you to the MET before you made it to the secatuers.
 
can someone tell me whats the difference between an IR test and and r2 test and a long lead test ? To my thinking the r2 test is a continuity performed at low voltage with a long lead ,whereas an insulation is at 500v , but whats the IR test?
 

Reply to Bonding the array in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi again. Right, I am seeing very mixed reactions and comments about the below question, I am just hoping to find a basic answer and reference...
Replies
4
Views
3K
Just been read through this and it says: How to determine if it’s an extraneous-conductive-part For this, a simple measurement is undertaken...
Replies
40
Views
21K
Hello there all, I'm a fairly newly qualified electrician and have been doing more and more EICRs lately, if someone could actually trawl through...
Replies
7
Views
3K
L
Hello all, Perhaps a few of you could help my understanding of the following query. The situation I am about to describe is purely hypothetical...
Replies
8
Views
8K
Loubanez
L
I've had my work assessed which has raised a question about Extraneous-conductive-part. I just want to be sure I fully understand this. BS7671...
Replies
12
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock