I have a client with what appears to be an intermitent fault on the lighting, but trips the power.

The installation has a 16th edition board with sockets on the RCD side, and lighting on the other side as usual.

Occasionally when the landing light is switched the RCD trips on the socket side. Would a borrowed neutral cause this. The lighting circuit itself has RCBO on it that doesn't trip; does the RCBO have anything to do with it.

I haven't checked for a borrowed neutral on the lighting yet, but even if there was one I can't see why that would affect the other RCD side.

Many thanks in advance
How old is the wiring (not the DB).?
Is the landing light on a 2way switch set up.?

Is there only one single module RCBO for the light or 2. ? ( upstairs & downstairs) ?

Let me know
 
My guess is that the wiring is late 60s early 70s.

The landing is 2 way, and the hall is 2 way. Both are on the same RCBO which never trips, only the RCD on the socket side of the board.

As I’ve combined all the circuits into one and put them on the RCD side I thought that would eliminate any possible cross connection/borrowed neutral.

So I’m looking at a fault rather than a cross connection I think.
 

Attachments

  • IMG_4234.jpeg
    389.5 KB · Views: 33
It may the the photo....but double check the count of live conductors vs neutral conductors on the RCD side.

Both are on the same RCBO which never trips,
Side thought - does that RCBO actually work?

Have you tried turning everything off and checking continuity between the N bars, and continuity between the top of each breaker ( in the off position) and the top of every other breaker?

Normally if there's a N-E fault on the RCD side and another unknown load driving current through the fault, the load in question would have to be connected 'somehow' to downstream of the RCD.

But a minor N-E fault on the RCD side, and a N-E fault on the non-RCD side can cause fun, e.g. a cooker element, or even that lighting circuit if the RCBO doesn't work.

Being honest as it's a Protek CU with a Volex RCD and a Niglon RCBO, it might be quicker to start again with a DP RCBO board fully testing each circuit and checking for interconnections as you go. Even if you miss the fault the DP RCBO's will show you where the problem is. I understand that budget may not allow this though.
 
My guess is that the wiring is late 60s early 70s.

The landing is 2 way, and the hall is 2 way. Both are on the same RCBO which never trips, only the RCD on the socket side of the board.

As I’ve combined all the circuits into one and put them on the RCD side I thought that would eliminate any possible cross connection/borrowed neutral.

So I’m looking at a fault rather than a cross connection I think.
Why are there so many different Manufacturers Breakers in the DB.??
 

Reply to Borrowed neutral on split load board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
419
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
406
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock