- Reaction score
- 5,607
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms.
This could have been a coincidence, but I disconnected both neutrals from the neutral bar (i.e the kitchen lights and sockets) and tested between them. They showed continuity (0.97 ohms). Just FYI, there was no continuity with these neutrals to the neutrals of the other circuits.
This is a dual RCD board. K lights and sockets on the same side.
Does the fact the neutrals showed continuity mean this is a borrowed neutral? I have not come across continuity between neutrals before. Is this the correct test for them? Does it actually mean they are connected together somewhere, or am I missing other possibilities?
Also, as the neutrals have been connected together somewhere in the house between these 2 circuits, how do I find this join? The house is full of shoddy DIY alterations. I would like to offer at least a guess as to how you find this join, but for the life of me I cannot think of a way.
This could have been a coincidence, but I disconnected both neutrals from the neutral bar (i.e the kitchen lights and sockets) and tested between them. They showed continuity (0.97 ohms). Just FYI, there was no continuity with these neutrals to the neutrals of the other circuits.
This is a dual RCD board. K lights and sockets on the same side.
Does the fact the neutrals showed continuity mean this is a borrowed neutral? I have not come across continuity between neutrals before. Is this the correct test for them? Does it actually mean they are connected together somewhere, or am I missing other possibilities?
Also, as the neutrals have been connected together somewhere in the house between these 2 circuits, how do I find this join? The house is full of shoddy DIY alterations. I would like to offer at least a guess as to how you find this join, but for the life of me I cannot think of a way.