During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms.

This could have been a coincidence, but I disconnected both neutrals from the neutral bar (i.e the kitchen lights and sockets) and tested between them. They showed continuity (0.97 ohms). Just FYI, there was no continuity with these neutrals to the neutrals of the other circuits.

This is a dual RCD board. K lights and sockets on the same side.

Does the fact the neutrals showed continuity mean this is a borrowed neutral? I have not come across continuity between neutrals before. Is this the correct test for them? Does it actually mean they are connected together somewhere, or am I missing other possibilities?

Also, as the neutrals have been connected together somewhere in the house between these 2 circuits, how do I find this join? The house is full of shoddy DIY alterations. I would like to offer at least a guess as to how you find this join, but for the life of me I cannot think of a way.
 
I'd say it's a fairly safe bet that with 0.98ohms between neutrals which have been disconnected from the neutral bar that you have a borrowed neutral.

I'd start by looking for any obvious DIY additions, like outside lighting or similar where someone could have picked up a live from a switch, not realising there is no neutral there and just run a neutral from the nearest socket.
You may find that this is also the location of the low IR fault.


You could disconnect a socket from the ring and split the ring into two halves. Test the neutral of each half to establish which half has the borrowed neutral connected.
Split that half of the ring again and repeat until you have narrowed down the location.
 
Is the IR still 0.10 with all neutral conductors for those circuits disconnected.
Yes. K lights removed (neutral) and sockets (neutral) removed from neutral bar. They then both test as 0.1Mohms to earth. Obviously both test the same as the N's have continuity. Liikely only one circuit actually has an IR fault, but I wont know until I find the join
 
Last edited:
I'd say it's a fairly safe bet that with 0.98ohms between neutrals which have been disconnected from the neutral bar that you have a borrowed neutral.

I'd start by looking for any obvious DIY additions, like outside lighting or similar where someone could have picked up a live from a switch, not realising there is no neutral there and just run a neutral from the nearest socket.
You may find that this is also the location of the low IR fault.


You could disconnect a socket from the ring and split the ring into two halves. Test the neutral of each half to establish which half has the borrowed neutral connected.
Split that half of the ring again and repeat until you have narrowed down the location.
In your example. If the line had been taken from a switch on the lighting circuit and the neutral from a nearby socket, how would that show continuity between neutrals? I realise there will be a resistance figure showing up between L and N as not all loads will be disconnected, but are there any appliances that would be as low as 0.97ohms? A halogen bulb for example would be around 90ohms. If there are such appliances then the culprit will be something as you suggest, otherwise the neutrals from both circuits are actually connected somewhere (I can't think of a reason why this would have happened though, meaning your example is far more likely, as long as it's possible to get such a low reading between L and N).

The fault finding is exactly the same as for an IR fault! Of course, simple, thankyou. Yes, I may well find the IR fault in the same location, at least hopefully I will.
 
First place I’d look would be the two way lighting for the stairs, if you have them. Any dodgy wiring in and around kitchen cabinets etc?
 
First place I’d look would be the two way lighting for the stairs, if you have them. Any dodgy wiring in and around kitchen cabinets etc?
2 way lighting seems to come up alot with borrowed neutral when reading other threads, but this is with the sockets. Kitchen cabinets certainly worth a look as it's all DIY.
 
With a long lead (resistance calibrated out) you could measure from the lighting N to he N at various sockets on the socket circuit. The resistance will decrease as you get closer to the point of interconnection (I'm assuming only one point, as more than one will complicate things). You could also repeat the other way round, and find the lighting point closest to the point of interconnection.

NB: disconnect the N of both circuits from the N bar first!
 
With a long lead (resistance calibrated out) you could measure from the lighting N to he N at various sockets on the socket circuit. The resistance will decrease as you get closer to the point of interconnection (I'm assuming only one point, as more than one will complicate things). You could also repeat the other way round, and find the lighting point closest to the point of interconnection.

NB: disconnect the N of both circuits from the N bar first!
Interesting idea. I guess you would need to have an idea of the layout though. It could help with an indication of the area though, as you say.
 
What does everyone think about the actual figure of 0.97ohms? Could this be a borrowed neutral (In which case the figure 0.97 ohms must be going through the load somewhere) or with a figure that low does it have to be 2 neutrals actually connected?
 
From your description, I'd say neutrals are directly connected together somewhere. IME not many loads have very low continuity across them like that (I think perhaps a compressor might be one example).

If they were connected through a load, it would likely have to be through 2 loads. Eg N1 - load1 - L - load2 - N2. But then you're measuring continuity across 2 loads, unlikely to be very low.

Or if N1 - load - N2, then the load wouldn't work as no potential difference across it. Again, unlikely.
 
Would seem to be directly connection somewhere

An interesting one I had a few years ago, the L&N from a PIR on a socket circuit was connected to a L&N from a light circuit at an outdoor light. Intent was the light switch overrode the PIR when required. The N was always interconnected, while the L connections only got interconnected when the PIR operated and the light switch was on at the same time!
 
Well this is looking like an odd one then.

What possible reason could there be for an actual neutral connection between lights and sockets! I suppose the DIY homeowner could have just got confused with a few junction box and put all the black conductors together.

I shall update when I find it.
 
What possible reason could there be for an actual neutral connection between lights and sockets!
I think this one is highly likely to be two sources of supply to something.

I like the idea mentioned of using a wander lead and checking sockets neutral to lighting points, and finding lowest reading, then checking lighting neutral to sockets neutrals and finding lowest reading. In theory you are then have the two joined points.
Otherwise, breaking down the sockets circuit won't take long.
Good luck!
 
With the two circuit CPCs separated [removed from the earth bar] do you still have the very low reading between the neutrals ?
That's an interesting point Dave. I'm afraid the cpcs were still in the MET. I should have tried with them out. I got a minor ticking off from @westward10 some years ago for IR testing without the cpcs in the earth bar and now its second nature to leave them in. Of course, during fault finding it would be fine, even necessary to remove, so that you get more information.

That was a pretty long winded way of saying...I didn't do it.
 
The test with the CPCs disconnected would be mainly to find out whether the N-N fault is actually a manifestation of two N-E shorts, one on each circuit, linking the neutrals together via the CPCs. However, we already know that there are no solid N-E shorts, only that 0.1MΩ that drew your attention in the first place. So while a test with disconnected CPCs might help trace the low IR, it won't shed any light on the N-N interconnection.

Returning to the original title and the following comment:
In your example. If the line had been taken from a switch on the lighting circuit and the neutral from a nearby socket, how would that show continuity between neutrals? I realise there will be a resistance figure showing up between L and N as not all loads will be disconnected, but are there any appliances that would be as low as 0.97ohms?

This observation is bang on the money. An N-N resistance of an ohm or two involving a lighting circuit is not going to be a borrowed neutral because no load will have such a low resistance, and a simple borrowing puts two loads in series between N-N as per @Pretty Mouth. The lowest load resistance one is going to encounter in a domestic environment is likely to be a large motor or transformer of a few ohms - saw bench, welder etc. - or a shower at half a dozen, but these are the exceptions.

An accidental interconnection of two lighting neutrals is quite easy to visualise in a system with assorted junction boxes but it's harder to see why a socket-outlet circuit would be involved if only because the meeting of 2.5mm² and 1.0 or 1.5 is likely to draw attention. Lights fed from a fused spur tangled up with the normal lighting circuit? Central heating controls? Extractor fan? Automation? Floorboard nail through two cables?
 
Mad idea - as there are two N paths back, two resistances in parallel, would putting mA clamp meter on the socket neutral and turning each light on in turn result in the highest reading when the lowest resistance path is increasingly in use?
The low power consumption of modern LED bulbs might make this idea a non starter….
There also may not be a material difference between the ‘wrong route’ and the higher resistance path of the smaller cable that is the correct route.
 
Mad idea - as there are two N paths back, two resistances in parallel, would putting mA clamp meter on the socket neutral and turning each light on in turn result in the highest reading when the lowest resistance path is increasingly in use?
The low power consumption of modern LED bulbs might make this idea a non starter….
There also may not be a material difference between the ‘wrong route’ and the higher resistance path of the smaller cable that is the correct route.
They are good points. I hate "Borrowed neutrals " so much !
 
In theory any test that can be done using load can also be done dead using resistance, and as a dead test that ought to be preferred, however the load test might involve less disturbance of the fittings.

As the lighting circuit is a radial, as the load is moved away from the CU towards the spurious interconnection, the lighting circuit neutral at the CU will receive a lower fraction of the load and the socket circuit neutral an increasing fraction. Once the interconnection point has been passed, the ratio will remain constant. It would be easier to apply a heavy load at a socket, but the ring configuration will complicate interpretation of the readings obtained.

As a reminder for anyone who hasn't read the whole story so far, the fault in the thread is seemingly not a borrowed neutral but a direct interconnection or fault between the neutrals of two circuits. A borrowed neutral is specifically the situation where a load is connected between the line of one circuit and the neutral of another.
 
I've had a think about the fault finding aspect. I just think I'm going to get in to a pickle trying to use a wander lead every where and relying on very small decreases/increases in resistance through a long (very unreliable) wander lead.

I like @davesparks method. I'e what i always believe to be the standard way of finding an IR fault.

I remove all the suspect (x3) neutrals from the bar in the CU. I split the ring somewhere. Test for continuity between socket neutral and lighting neutral in the CU. Only one of the socket neutrals should now show continuity. Liven up the side that doesn't show continuity and every thing that works is removed from the suspect list. However, if the fault/join is in a JB then that means you can't rule out one of the cables in the actual socket you have split the ring in, so I always keep a record of which sockets I have made the split at, until of course they have been ruled out by making a split elsewhere.

I think this is either going to be an easy find on the kitchen lights as they all look dodgy, or.... it's going to be horrible!

The 80 year old, former senior civil engineer client continuously likes to get involved and believes he has a grasp of electrics. He doesn't. Whenever I try and explain something to him (because he has asked), he says 'yes, yes I know that, I was a civil engineer you know'. He then explains it to his wife (wrongly). I absolutely cringed when she asked him a question and he replied 'you don't need to worry your pretty little head about it'. I think he's still living in the 50's. He didn't say it in a mean way, it appeared to be just standard speech between him and his wife. Scary.
 
I remove all the suspect (x3) neutrals from the bar in the CU. I split the ring somewhere. Test for continuity between socket neutral and lighting neutral in the CU. Only one of the socket neutrals should now show continuity. Liven up the side that doesn't show continuity and every thing that works is removed from the suspect list.

having split the ring I'd do a basic wander lead continuity test between the lighting N and N at every socket. (plug in lead)
No continuity = ruled out.
Continuity = take socket apart and try both N's in that socket. Rule more out. Rinse and repeat.

I think that's the fastest way.
Walk around with an electric screwdriver, you'll be home for afternoon tea! Best of luck....
 
I like @davesparks method. I'e what i always believe to be the standard way of finding an IR fault.

Nothing wrong with that, but I'd take advantage of the known continuity of the ring to save opening and disconnecting stuff. I would inject a current around it from a small ELV benchtop power supply that can operate in constant-current mode into a short-circuit.

First I would go to the CU and hook up the PSU to circulate say 5A around the ring neutral from leg A to leg B. I would tie the ring line to neutral at leg A so that the voltage along the neutral can be read at every socket without a wander lead, just by plugging in a voltmeter with a 13A plug adaptor. Each metre of run between CU leg A and the socket would add 38-40mV to the reading.

First I would measure the voltage between leg A neutral and the lighting neutral at the CU, test (A) in the sketch, to find out the voltage present on the ring neutral at the point of the interconnection. Then I would walk around the ring doing test (B) with the plug adaptor, looking for a socket showing the nearest voltage to test (A), which would be at the point of interconnection. Or, if it's midway between two sockets, those with the nearest voltages above and below test (A).

At this point you will know the location of the problem on the ring without having to access any lighting points. If it's not then obvious which lighting point is involved, it would also be possible to do the same test using VD along the lighting circuit, but it would need shorting L-N at the far end or a wander lead running out to it, to serve in the same current injection role as leg B of the ring.

This probably sounds a bit long-winded but I would say with a dozen points on each circuit, so long as I could get to the sockets and lampholders / roses, I would guarantee to have found the nearest point to the interconnection within 20 minutes, without undoing a single screw other than to open the CU. Although the PSU would be 'energising' the circuit, it would only be with a volt or two, so none of the tests would be hazardous. It would not matter if a few small hidden loads remained connected to the circuits.

In another thread I will tell how I used this method to trace a fault in a completely inaccessible circuit with 20 points, on location on the beach in Amalfi, using a brake light bulb and an alarm battery as my constant-current source.

trace erroneous.png
 
An accidental interconnection of two lighting neutrals is quite easy to visualise in a system with assorted junction boxes but it's harder to see why a socket-outlet circuit would be involved if only because the meeting of 2.5mm² and 1.0 or 1.5 is likely to draw attention. Lights fed from a fused spur tangled up with the normal lighting circuit? Central heating controls? Extractor fan? Automation? Floorboard nail through two cables?
Anything is possible with some 'kitchen engineers'.
 
Last edited:
Maybe they both have neutral/earth IR faults hence the apparent connection between them. Have you done a continuity test between neutral/earth.
The test with the CPCs disconnected would be mainly to find out whether the N-N fault is actually a manifestation of two N-E shorts, one on each circuit, linking the neutrals together via the CPCs. However, we already know that there are no solid N-E shorts, only that 0.1MΩ that drew your attention in the first place. So while a test with disconnected CPCs might help trace the low IR, it won't shed any light on the N-N interconnection.

 
This N-E test stuff is all old news, see my post #19. There is unusually low insulation resistance between neutral and earth but not a short, so whilst it needs finding it's not the reason that the two neutrals show a hard short together. It might be further evidence of some cables nailed together or co-located with the N-N problem though.
 
In your example. If the line had been taken from a switch on the lighting circuit and the neutral from a nearby socket, how would that show continuity between neutrals?

Sorry, that was my mistake, I didn't fully think that one through!

I was at the time bored at work watching the special effects people (plumbers) ruin a perfectly good stage floor with their rain effects.
 
Last edited:
Ive had 2 o these no so long ago.
One was a conservatory light where they had wired live from a nearby two way switch and taken the neutral from the socket below.
Second was kitchen under unit lights same wiring.
Id be looking around trying to spot the red flags first, opening some accesories should help you identify the culprit.

Good luck.
 
This is different though. It's not a line from one circuit paired with a neutral from another, it's two different neutrals connected together. It's not something you would do even as a bodge and might be a true fault e.g. a screw through two cables.
 
This is different though. It's not a line from one circuit paired with a neutral from another, it's two different neutrals connected together. It's not something you would do even as a bodge and might be a true fault e.g. a screw through two cables.
Absolutely possible, but just seems so unlikely. A screw passing perfectly through 2 cables, missing the earth on both (which is probably centred in the middle of the cable) and touching both neutrals.
I suppose it has to happen one in a million times, so perhaps this is it. I'd rather have won the lottery!
 
Absolutely possible, but just seems so unlikely. A screw passing perfectly through 2 cables, missing the earth on both (which is probably centred in the middle of the cable) and touching both neutrals.
I suppose it has to happen one in a million times, so perhaps this is it. I'd rather have won the lottery!
I had a lighting cable, a twin and earth used as a pair of strappers between 2 way switching, damaged by a nail for a dado rail. It nicked one of the strappers and caused a live to earth fault. Only the strapper was nicked, not the cpc. Fault finder was complicated by which where the two switches were operated.
 
It's proving difficult getting a date to do the fault finding, so I'm afraid there won't be an update any time soon. I will update though when I've been back.
 
This is different though. It's not a line from one circuit paired with a neutral from another, it's two different neutrals connected together. It's not something you would do even as a bodge and might be a true fault e.g. a screw through two cables.
I dont think so! Keep taking the pills if you think a screw has gone through 2 different cables. Im assuming you dont do much domestic stuff.
 
I dont think so! Keep taking the pills if you think a screw has gone through 2 different cables. Im assuming you dont do much domestic stuff.
What he means is there are two different scenarios:
A) no neutral there at all so one is stolen from elsewhere (like your conservatory light example)
B) two neutral conductors from different circuits are joined (what this thread is about and not really a borrowed neutral. All my ideas for what we could call this don’t get past the language filter….
 
I dont think so! Keep taking the pills if you think a screw has gone through 2 different cables. Im assuming you dont do much domestic stuff.
I've seen where someone has put two cables one on top of each other to save on clips, notched in under floorboards, so it's certainly possible.
 
Last edited:

What he means is there are two different scenarios:
A) no neutral there at all so one is stolen from elsewhere (like your conservatory light example)
B) two neutral conductors from different circuits are joined (what this thread is about and not really a borrowed neutral. All my ideas for what we could call this don’t get past the language filter….
That is more of an interconnection than a borrowed neutral IMO
 
Last edited:
A pair of cables running along a ceiling joist could both get penetrated.
Hanging a light fitting, if you used long screws and only caught the edge of the joist you could easily cause an N-N short, and maybe also cause a resistance to the CPC at the same time.

The same goes for cables in partitions.


A bit more info on the type of house/size etc maybe of help.
 
Well, I must apologise as I shall not be returning to the customer, so I will not be able to update. I've just had the most odd conversation with him on the phone and he does not want me back. Bit shocked as that hasn't happened before. As in the opening post, he was a very difficult man to deal with but I wasn't expecting that.

His reasons were that I miss diagnosed a faulty cooker and I left the loft lights on!

I'm not a 100% sure I didn't miss diagnose the cooker. The cooker itself showed 0.1Mohms N-E. Is this perhaps acceptable for some cookers? Its an older looking rangemaster. Even so, bit harsh!

Happy not to be going back though, he was a very un pleasant man and shockingly rude to his very pleasant wife.

Oh yes, and he isn't going to pay for the 2 hours fault finding or fixing his 3 kitchen lights. I will not be going to the small claims for a £100 and shall take it on the chin, albeit a little grumpily :)

The neutral problem will remain and we shall never know!!!
 

Reply to Can I confirm how to test for and how to find a borrowed neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
913
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
513
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
684
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock